Larry, Pitfalls ?
The biggest pitfall I would say is if you have a VERY stiff grid.

If your Voc is say, 170V DC and the CC current limits it output at say, 169 V DC, they you are going to need to add an input power resistor of a couple Ohms to help cushion the input to be more like a PV module. A lot of times, the grid is
not nearly this bad, especially generators.

Also, If you are going to do this, I would NOT use Solar mode but instead try Hydro mode set to Manual MPP voltage. First start the MPPV at something just less than Voc or maybe, say, 160 VDC. Then, from main STATUS screen, you can
adjust the input voltage up and down by pressing the Soft-Right or Soft-Left
keys respectfully. (upper right and upper left keys). Then you can manually get
a feel for what it should be set for.

The Classic 200 is the only CC of ours that I would use. The 250 would work but the 200 is much more suited. I wish there were a real charger that one could buy that was isolated, and we have never really advocated MPPT charge controllers for this but in a pinch, they always seem to work find. Never did add a "DT" mode (after Daryl
Thayer of course), but this hydro mode seems to work OK.

If you want to let it sweep but setting it to 3 minutes (or higher) that will also work. If you do that, set the minimum input voltage. Something like 140V or so will keep it from dropping the input voltage too low and either bogging down the input source
and the rectifier bridge (especially generators)

You can also set the INPUT current limit in the LIMITS menu. This was for hydro
in particular.  Either limit can help reduce Isc or bogging down issues.

The other pitfall is that it is NOT galvanically isolated so you should be very careful. We use an X240 equivalent transformer to keep the batteries going in our burn in
rack using 2 Classic 200s and it works great.

Also, use a nice and strong full bridge rectifier so that it applies 120 Hz instead of 60 Hz to the input. That is much easier on the input capacitors and things and just makes it work smoother. There are input capacitors (filtering) on most charge controllers.

Again, in a pinch this seems to work but watch that input max power point voltage to make sure it is not too high compared to the Voc. If there isn't enough voltage spacing between the two (stiff AC source) then the control isn't going to be very smooth and might risk
letting the smoke out.

What ever you do here, be very careful what you touch !

boB





On 12/16/2014 6:39 AM, Larry wrote:
I must have missed the prior discussion about using PV CC. The concept sounds good but how many of you have done this and are there any pitfalls to be aware of? If I use a 20 amp bridge I should be able to produce 80 amps @ 14.4V. For continuous operation, will I need a large heat sink on it?

How does the unfiltered full wave peak voltage affect the CC over time? Are they (specifically Midnite) really designed to handle input waveform like this? I like this idea, especially if I can stack the controllers.
Thank you,

Larry
On 12/15/14 6:51 PM, jay peltz wrote:
Hi Kirk,

If you use a 200vdc midnight CC you'll have no issues.
When you rectify 120vac its up around 166vdc
( uses the peak vac which is around 170vac.)

For a 150vdc max controller ( midnite 150) or a 144vdc ( outback FM) then a buck transformer or standard transformer is the trick to reduce the AC and hence the DC for these lower voltage units.

jay
peltz power
On Dec 15, 2014, at 5:38 PM, Kirk Herander wrote:

This has been discussed on this list in years past. It is possible to use an outback charge controller as a battery charger. You need to put the 120 AC into a bridge rectifier, then feed the 120 DC into the controller's PV input. So you'll have an 80 amp battery charger.
*Kirk Herander*
*VT Solar, LLC*
*/Proven PV provider since 1991/*
*www.vermontsolarnow.com*
dba Vermont Solar Engineering
NABCEP^TMInaugural Certificant
VT RE Incentive Program Partner
802.863.1202
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of*Dan Tittmann
*Sent:*Monday, December 15, 2014 8:18 PM
*To:*i...@windsine.org <mailto:i...@windsine.org>; RE-wrenches
*Subject:*Re: [RE-wrenches] Programmable Battery Charger
You can manually adjust Iotas with tweaking the potentiomiters while monitoring it with a god volt meter. But no time adjustment.
Daniel

Daniel Tittmann
CTO
Greenwired
www.greenwired.com <http://www.greenwired.com>
dan...@greenwired.com <mailto:dan...@greenwired.com>
707-923-2001 (office)
707-206-5088 (Cell)
On Mon, Dec 15, 2014 at 4:21 PM, Windsine Inc. <winds...@gmail.com <mailto:winds...@gmail.com>> wrote:

Check out Argus Technologies.

RoyR

On Dec 15, 2014 4:01 PM, "Larry" <la...@starlightsolar.com <mailto:la...@starlightsolar.com>> wrote:

Wrenches,

Does anyone know of a 120/12 volt battery charger that can be programmed for absorb and float voltage and time in absorb mode? I have been needing this product for many years but I can only find it in inverters with built in chargers from Magnum, Outback, and Xantrex.

--
Thank you,

Larry Crutcher
Starlight Solar Power Systems



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to