Have you tried it without the balancing transformer? You described that the voltage waveform looked good, but the current waveform had distortion. I would take the X 240 out of the system, and see what happens. I hardly ever use the balancing transformers, and I never let the inverters go into search mode anymore. With search mode set to actually work with all loads, it usually pulls about 10 to 15 watts/ inverter, while actual run is 20 watts. It just never was worth all the extra hassle and cost of the X 240, IMHO.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 12/1/2014 7:57 AM, d...@foxfire-energy.com wrote:
Yes, running on gen set was the first thing we tried. Breakers were off on all units initially. The first unit we lit tripped out on some random error, but the other two lit up fine. After a few min of breaker off, the first one tried to light up, but the genny couldn't handle all three at once (80's vintage 5k propane Onan -- the most we could get out of it without pulling the voltage out of spec was 10A @240vac).

We switched back over to the RE system and everything ran just fine. We measured 14aac at full draw. That's when we discovered the units all run properly (on RE) if you either leave them on all the time with the temp turned down or briefly turn them off (with the remote controller) for a short time. Not sure, but it looks like somewhere around 4 hours of off from the controller is when the comm/relight problem happens. Mitsubishi is now talking about using a different controller to reduce the standby draw (So they can stay on all the time), but it sounds like they'd still like to blame the RE system. I'm still thinking bad sushi.

db

Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
NABCEP #092907-44


    -------- Original Message --------
    Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback
    VFX Off Grid
    From: jay peltz <j...@asis.com <mailto:j...@asis.com>>
    Date: Sun, November 30, 2014 8:12 pm
    To: RE-wrenches <re-wrenches@lists.re-wrenches.org
    <mailto:re-wrenches@lists.re-wrenches.org>>

    HI Dan,

    Have you tried this on a different power source, say generator etc?
    You might also try a different inverter brand just to make sure.

    I once had radio noise from a magnum, some years ago.  Tried
    everything, in the end, I swapped it for a VFX and the problem was
    gone, customer was happy.

    And I'm going to agree with Mitsubishi, most likely the inverter.
    The OB/FX just isn't compatible with some machines.

    jay

    peltz power
    On Nov 30, 2014, at 4:29 PM, <d...@foxfire-energy.com
    <mailto:d...@foxfire-energy.com>> <d...@foxfire-energy.com
    <mailto:d...@foxfire-energy.com>> wrote:

    We're still not at the bottom of it. Seems Mitsubishi is doing
    their level best to finger the RE system. Yes, the current wave
    form (On a Fluke 43 Power Analyzer) has a shoulder.. looks down
    right funky on one inverter thru the X240 until the 2nd inverter
    lights. Current also looks funkular when each mini split is lit
    (Pulses).. Still, I'm thinking it's more about how the mini
    splits toke power rather than how the Outbacks produce power. The
    voltage waveforms look fine.
    the other chin scratcher is that it seems this model of mini
    split has only been around since spring. There might be a model
    specific cold weather setup the AC folks missed. Something about
    a jumper on a control board that needs to be snipped to enable
    the compressor heater.

    We also noticed that all mini splits work just fine if you leave
    them on and turned down.. But that kind of power draw for folks
    that have been loving off grid since 92 is just unacceptable.
    (these guys were turning off GFI breakers because they could see
    a draw).

    Either way, the power system itself is working fine as is
    everything else in the house. And no, the new power system has
    not kept the lawn mower from starting or the dog from eating the
    cats food.

    Peace. db

    Dan Brown
    Foxfire Energy Corp.
    Renewable Energy Systems
    (802)-483-2564
    www.Foxfire-Energy.com <http://www.Foxfire-Energy.com/>
    NABCEP #092907-44
    <sigimg0.png>


        -------- Original Message --------
        Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting
        with Outback
        VFX Off Grid
        From: Wayne Irwin <wa...@pureenergysolar.com
        <mailto:wa...@pureenergysolar.com>>
        Date: Tue, October 21, 2014 8:52 pm
        To: Wrenches <re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>>

        We have found that the mini-splits have only had issues while
        gen sets are running.
        In some cases (when on genset) the mini's will run
        irregularly or flash a fault status.

        Rather than try to have the mini's run on gen power we
        install dc chargers to charge batts from gen power.

        My thought is that the AC Installer either has something
        wrong or the Mitsubishi's have very tight parameters.
        Be sure that the wiring from the inside unit to the outside
        unit are correct. Should be only three wires (plus gnd). Very
        easy to check.

        Possible alternative solution would be look into the cost of
        installing a Gree since they are the least expensive.



        Wayne Irwin,
        President
        License #CVC56695
        State Licensed Solar Contractor
        Pure Energy Solar International Inc.
        wa...@pureenergysolar.com <mailto:pureenergyso...@hotmail.com>
        http://PureEnergySolar.com <http://PureEnergySolar.com/>
        http://SolarChargingStation.net
        <https://solarchargingstation.net/>
        352 377-6527 Office
        352 336-3299 Fax
        352 316-1637 Cell

        The Sun Is Always Shining!

        The content of this message is Pure Energy Solar
        Confidential. If you are not the intended recipient and have
        received this message in error, any use or distribution is
        prohibited. Please notify me immediately by reply e-mail and
        delete this message from your computer system. Thank you.


        ------------------------------------------------------------------------
        Date: Tue, 21 Oct 2014 11:23:31 -0600
        From: r...@solarray.com <mailto:r...@solarray.com>
        To: re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>
        Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting
        with Outback VFX Off Grid

        The Outback is not a perfect Sinewave.  It still has tiny
        steps in the wave, and when electronics have a problem, its
usually with the wave form as it crosses zero voltage . Instead of being instantaneous, it has a few milliseconds of
        time the wave is at the zero crossing, which can drive some
        electronics nuts.  I don't understand the issue beyond that,
        but apparently the electronics use the zero crossing for
        timers and synchronizing, and they're looking for an instant
        "click", not a smear.
        Do the heat pumps work with the generator?  Even though
        generators can have more harmonic distortion, they do usually
        have a clean zero crossing.
        If this is the case, I'm afraid I don't have a cure.  We used
        to use capacitors, but Dan from Exeltech just poo pooed that
        fix in another recent thread, so I don't have any other
        tricks up my sleeve.

        R.Ray Walters
        CTO, Solarray, Inc
        Nabcep Certified PV Installer,
        Licensed Master Electrician
        Solar Design Engineer
        303 505-8760

        On 10/21/2014 8:54 AM, d...@foxfire-energy.com
        <mailto:d...@foxfire-energy.com> wrote:

            Anyone else had issues with Mitsubishi Mini Split heat
            pumps fighting with Outback VFX off grid inverters?
            Everything is brand new. Outback VFX7248, three separate
            heat pumps. The heat pumps shut down reporting multiple /
            confusing input commands. The heat pump guys want to
            blame the power system. I'm thinking bad Sushi. Thanks db


            Dan Brown
            Foxfire Energy Corp.
            Renewable Energy Systems
            (802)-483-2564
            www.Foxfire-Energy.com <http://www.Foxfire-Energy.com/>
            NABCEP #092907-44
            <ATT00001.png>


            _______________________________________________
            List sponsored by Redwood Alliance

            List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
  
<http://www.mail-archive.com/re-wrenches%40lists.re-wrenches.org/maillist.html>

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org  <http://www.members.re-wrenches.org/>



        _______________________________________________ List
        sponsored by Redwood Alliance List Address:
        RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org> Change listserver
        email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        List-Archive:
        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
        List rules & etiquette: www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm> Check out or
        update participant bios: www.members.re-wrenches.org
        <http://www.members.re-wrenches.org/>
        ------------------------------------------------------------------------
        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to