Kirk:

A DC grounding electrode conductor (GEC) is not required for inverters that do NOT have a ground reference for the PV+ and PV- conductor(s) from the PV array.

A GEC is not required if the string inverter is one of the new TL (transformerless) types. Also, this applies to micro-inverters such as the new Enphase M250 and later versions of the M215.

Where this applies, only a properly sized equipment grounding conductor (EGC) is required.

The EGC is sized according to [NEC 690.45] and can be a minimum of #14AWG when not exposed to damage, or #6AWG when exposed to potential damage.

Regards,

Gary Willett PE
Icarus Engineering LLC

On 10/28/14, 12:53 PM, Kirk wrote:
Hi,
I'm on a jobsite without my code book. Could someone tell me where in the code 
ungrounded systems do not require the inverter GEC? Basically my onsite 
electrician doesn't believe me. Thanks.

Kirk Herander
VSE
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to