Wrenches, 

Be careful about connecting *any* capacitors across an inverter's AC output.  
It's not a smart thing to do.

While a capacitor may help in some cases when a load has a substantially poor 
power factor due to significant inductance, there are two serious concerns here:

1. The power factor seen by the inverter will be equally bad in the opposite 
polarity when the inductive load turns off, and IF the capacitor is still 
connected across the lines.  Larry implied the capacitor he connected was 
disconnected when the load turned off.

2. Larry "shot-gunned" a solution.  He guessed, and got lucky.  We don't know 
how much actual capacitance was needed in this specific situation.  Capacitors 
connected across an inverter's AC output can destabilize its voltage control 
loops, leading to erratic AC voltage, resulting in possible damage to the 
inverter, the load(s) .. or both.

Power factor is one of the most misunderstood aspects of electricity.



Dan
(Professional inverter design engineer .. among other things...)

--------------------------------------------
On Sun, 10/12/14, Starlight Solar Power Systems <la...@starlightsolar.com> 
wrote:

 Subject: Re: [RE-wrenches] Quantifying power quality
 To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
 Date: Sunday, October 12, 2014, 1:33 PM
 
Hi William,

If you recall a couple years ago we had some discussion here about a problem 
with a specific make appliance being powered by a Magnum inverter. The problem, 
it was discovered, was the appliance input PF was creating current demands that 
the transformer based inverter could not keep up with. When I powered the load 
with a low cost, high frequency inverter, it worked fine. Apparently the HF 
inverter can keep up with the current changes faster than the Magnum.

To fix the problem, a 50mf run type capacitor was installed in the appliance so 
that it was applied across the AC input when powered on. Everything worked fine 
then because the cap was taming the wild current created by the low PF. 

Try looking at the current and voltage waveform together (AC shunt, dual trace 
scope) at the UPS input. If the current is displaying large spikes and/or is 
out of phase, you may have found the problem is with a non linear load from the 
UPS. It may be the SI, like the Magnum, can not keep up and so the UPS input 
circuits are throwing a fit.

Or, something else you can try, connect a high frequency inverter and try to 
power the UPS. This can be a portable 12 volt battery and inverter. If the 
problem disappears, well, you take it from there.

Larry

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to