Are they single or three phase inverters? 

Connected on the load or supply side?

Brian

> On Aug 4, 2014, at 7:09 PM, Chris Mason <cometenergysyst...@gmail.com> wrote:
> 
> If you are using a load center to aggregate the inverter outputs, swap the 3 
> pole breaker for three single poles. Hopefully you can demonstrate only one 
> inverter works.
> If the UL listing tests and certifies for this, why do they need to do it in 
> the field? Next they will want you to set up a full lab test suite. 
> 
> 
>> On Mon, Aug 4, 2014 at 8:56 PM, Jerry Shafer <jerrysgarag...@gmail.com> 
>> wrote:
>> If you using a AC disconnect shut off power to it install a jumper on two of 
>> the legs just testing once inverter is back on line pull the switch and see 
>> what happens. Swap jumper location and tetest, once you tesy all legs remove 
>> jumper wires.
>> 
>>> On Aug 4, 2014 7:43 AM, "Rebekah Hren" <rebekah.h...@gmail.com> wrote:
>>> Al,
>>> I have witnessed this test in NC several times, but with medium voltage 
>>> connected systems, not systems connected to a building service.  A medium 
>>> voltage subcontractor used a disconnect stick to open one phase at a time 
>>> at the fused cutout point of delivery to the distribution network (on the 
>>> high side of the transformers) . We learned to do the test early in the 
>>> morning with the array divided in subsections to keep the current as low as 
>>> possible at the POD because there is an arc pulled when one phase is 
>>> opened. 
>>> 
>>> The phase current was being monitored during the test to insure that the 
>>> inverters stopped exporting current to the other two phases when one phase 
>>> was lost. 
>>> It's been awhile, so there may be a better/safer way to do this test for MV 
>>> connected systems now that I'm not aware of...would be happy to hear about 
>>> it if so. 
>>> 
>>> If this is a PV system connected to a building service this wouldn't be the 
>>> way to do this test.
>>> Cheers, 
>>> Rebekah Hren
>>> 
>>> 
>>> 
>>>> On Mon, Aug 4, 2014 at 11:24 AM, Allen Frishman <amfr...@aeonsolar.com> 
>>>> wrote:
>>>> Wrenchers,
>>>> The Ct Utility company CL&P requires the following as part of the 
>>>> verification test.
>>>> "Because this is a three-phase service, the witness test must also 
>>>> demonstrate that the inverter shuts down upon loss of each individual 
>>>> phase"
>>>> 
>>>> Any recommendations on how to do this test safely?
>>>> Al Frishman
>>>> AeonSolar
>>>> 
>>>> (917) 699-6641 - cell
>>>> (888) 460-2867
>>>> www.aeonsolar.com
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>> 
>>> 
>>> 
>>> -- 
>>> Tel: 336.266.8800
>>> NABCEP Certified Solar PV Installation Professionalâ„¢ 091209-85
>>> NC Licensed Electrical Contractor
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> 
> 
> -- 
> Chris Mason
> NABCEP Certified Solar PV Installerâ„¢
> Solar Design Engineer
> Generac Generators Industrial technician
> 
> www.cometsolar.com
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to