I have never seen an inverter that does not specify a OCPD size. 

Jay
Peltz power. 

Sent from my iPhone

> On Jun 26, 2014, at 3:20 PM, Dave Click <davecl...@fsec.ucf.edu> wrote:
> 
> Corey,
> 
> The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters are the 
> exception because they are specially listed to share a breaker. As for the 
> other inverters, doubling them up on a single breaker / disconnect probably 
> goes against their installation instructions [110.3(B)] and it's unlikely 
> that you could put multiple units on a single breaker anyway because when you 
> take (2 inverters) x (rated current) x (1.25) you will probably come up with 
> a minimum breaker size that is larger than the maximum allowed under the NRTL 
> listing to UL 1741.
> 
> Dave
> 
> 
> 
>> On 2014/6/26, 16:18, Corey Shalanski wrote:
>> We considered the necessity to shut down individual inverters and determined 
>> that the added costs of an inverter output combiner panel were not merited. 
>> I agree that in theory it seems beneficial to be able to switch each 
>> inverter individually, but how often does this occur in practice? For the 
>> relatively infrequent cases where we need to return to a jobsite and shut 
>> down an inverter - for troubleshooting/removal/etc. - we do not mind 
>> shutting down the other inverters (up to a limit) for what is hopefully a 
>> short period of time.
>> 
>> Again, this whole line of reasoning may be shown to be faulty if someone can 
>> directly point to the Code section that requires OCPD on each individual 
>> inverter.
>> 
>> --
>> Corey
>> ᐧ
>> 
>> 
>>> On Thu, Jun 26, 2014 at 9:20 AM, 
>>> <re-wrenches-requ...@lists.re-wrenches.org> wrote:
>>> 
>>> Message: 5
>>> Date: Wed, 25 Jun 2014 19:17:57 -0700
>>> From: William Miller <will...@millersolar.com>
>>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>> Subject: Re: [RE-wrenches] Combining Multiple Inverters
>>> Message-ID: <04f4b8fd-e280-4bf2-b5a4-c2fca8d1c...@millersolar.com>
>>> Content-Type: text/plain; charset="utf-8"
>>> 
>>> Not allowed. You need a dedicated OCPD. Plus seems like a really bad idea.  
>>> How do you shut down just one inverter?
>>> 
>>> 
>>> 
>>> Miller Solar
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to