Steve:

The PV is 200 feet away on the other side of a building. We have THWN in PVC 
conduit. This job was installed over 10 years ago. We don't want to repull all 
of the leads for 6 strings in PV wire. 

We Void splices like the plague but the PV leads terminated in a HU361 switch 
and we needed to splice on some short leads to make this work. 

Are you telling me we can no longer use 600 volt rated building wire and/or 
standard 600 volt rated wire nuts on PV circuits with your products?  If so, 
this is a BIG deal for installers. 

Thanks,

William

Miller Solar

> On Jun 24, 2014, at 8:52 AM, Steve Jefferson 
> <steve.jeffer...@sma-america.com> wrote:
> 
> Morning William,
> 
> You can contact me offline, or better yet, call our Service Line.  I checked 
> and see no calls in about AFCI issues.
> 
> Also, we don't recommend wire nuts on DC conductors (or AC) due to the 
> probability of unreliable and highly resistive connection.
> 
> Thanks 
> 
> SMA America, LLC
> Steve Jefferson
> Service Line Supervisor
> 3925 Atherton Ave
> Rocklin, CA 95765 - 3714
> U.S.A.
> Tel:  +1 916 625 3185 (direct)
> Fax: +1 916 625 0871
> Mobile: +1 916 622 4253
> Email: steve.jeffer...@sma-america.com
> www.SMA-America.com
> 
> 
>  
> This email and any attachments thereto may contain SMA America, LLC 
> confidential, privileged and private material for the sole use of the 
> intended recipient. Any review, copying, or distribution of this email (or 
> any attachments thereto) by others is strictly prohibited. If you are not the 
> intended recipient, please contact the sender immediately and permanently 
> delete the original and any copies of this email and any attachments thereto. 
> Thank you.
> 
> 
> 
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of William Miller
> Sent: Monday, June 23, 2014 3:40 PM
> To: RE-wrenches
> Subject: [RE-wrenches] AFCI disturbances.
> 
> Friends: 
> 
> We are starting to replace dying SB2500s with new units. The AFCI is giving 
> us fits with disturbances. We are told we can not even use wire nuts. 
> 
> Has anyone else dealt with this?  What have you learned?
> 
> Thanks in advance. 
> 
> William
> 
> Miller Solar
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to