Ray:

Darn good question, especially since I will be doing the exact same thing, 
*tomorrow*.
I have never been clear on the real problem. Fine stranded cables overheat in 
the wrong lugs?  Is this true for mechanical or compression?

Aside from code compliance, what is the best common sense approach to Sunny 
Islands with fine stranded?  Annual retorquing?  Pin terminals?  Solder tinning 
the strands?????

I used to wrap thin copper sheeting around fine stranded just to corral the 
strands. Is this a possible solution?

Thanks Ray for bringing up a question I forgot to consider. 

William


Miller Solar

> On Apr 29, 2014, at 10:48 PM, Ray Walters <r...@solarray.com> wrote:
> 
> Hi All;
> 
> In order to avoid any of my work showing up in someone's slideshow of 
> horrors, I'm trying to find the correct way to wire 3 Sunny Islands with 
> Cobra X flex cable.
> While it doesn't actually mention it in the SMA manual, a call to SMA tech 
> support confirmed my suspicions: the DC lugs in the inverter are NOT rated 
> for flex or fine stranded cable.
> Both SMA and CED recommended I try Grainger's for crimp on adapters.  
> Grainger had no clue, and nothing came up in searches there.
> From a trade show, I have an ILSCO lug book, that shows a crimp on pigtail 
> adapter.  It does not mention whether its flex rated though on the crimp side 
> of the adapter, as the adapter is used primarily to land over sized cables 
> into smaller lugs.  (2/0 to #1, for instance)
> The best I've found so far, is NSI, which makes sleeves, that are installed 
> around the wire, right in the connection:
> http://www.nsiindustries.com/products/electrical/connectors/compression-connectors/copper-compression/fsflex-cable-sleeve.aspx
> I also found a Schneider white paper recommending sleeves with their lugs:
> http://static.schneider-electric.us/docs/Circuit%20Protection/0515DB0301.pdf
> 
> So who has used these sleeves, and where do I get them?
> The sleeves seem like a decent compromise, whilst the ILSCO pigtail adapters 
> are coming in at $40/ ea...... (ouch)
> 
> On the internet, I'm seeing several examples of X flex used directly (no 
> adapters) with the Sunny Islands, so are folks just blowing off articles 
> 690.31(F) and 110.14, that specify the connector be rated for flex cable?
> And finally, couldn't SMA use a lug that was flex rated?
> For example, Marathon makes Class K rated mechanical Lugs: 
> http://www.marathonsp.com/NewRatings.html
> I'd use THHN, but I really don't feel good about wiring the Heineman breakers 
> with that stiff a wire.  I've cracked breaker cases before......that's why 
> the X flex is industry standard for off grid DC.
> 
> Thanks for your help,
> 
> -- 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to