Nathan,
The only explanation the electrical distributor provided is seen below. They 
are really skirting a thorough explanation...
The distributor engineer does not view the inverters as a negative load, and 
states they will exceed the 500A fault current limit the site is designed for.
Thanks,
Karl

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nathan Charles
Sent: Thursday, March 27, 2014 2:03 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fault Current

Karl,

Can you give us some more details on their concerns?  I've done some very large 
single phase ag installs and the only time I've had issues is when we exceed 
the 80% of minimum load on the medium voltage feeder.

Best,

-N

On Thu, Mar 27, 2014 at 2:51 PM, Karl Jaeger 
<kjae...@lightwavesolar.com<mailto:kjae...@lightwavesolar.com>> wrote:
Dave,
We are about as rural as we can get here.... farm land. Very good document, 
nonetheless.
Karl

From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of Dave Click
Sent: Thursday, March 27, 2014 1:29 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Fault Current

Karl, you're interconnecting into a spot/area network, right? It's a real 
concern; some solutions and background on the issue here:
http://www.nrel.gov/docs/fy09osti/45061.pdf

DKC
On 2014/3/27, 14:05, Karl Jaeger wrote:
Esteemed Wrenches,
We've recently run into an issue with a local distributor citing network fault 
current on a split-phase service as a reason to prevent interconnection of our 
customer's solar array. They've given us the options of reducing our system 
size from 36.5kW-DC to 15kW-DC, or having the customer upgrade to 3-phase at a 
soft price of $20-30K. We're looking at 32kW of inverters on a 167kVA 
transformer.

Does anyone have experience on circumventing the issue of network fault 
current? Any experience with Fault Current Limiters?

Much appreciated,

Karl Jaeger
Design/Build Engineer
LightWave Solar Electric LLC




_______________________________________________

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Change email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions
(717) 283-2021 direct
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to