Its Mexico, so its 60 Hz, 3 phase 120/ 208. I had originally considered the Radians for this project, until I went down and determined the actual voltage.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/26/2014 7:31 AM, Phil Undercuffler wrote:
You mentioned this is out of the country -- is it 230v line to neutral, or 120/208? OutBack's export Radian can do three phase, up to 72kW continuous.
HTH,

Phil




On Tuesday, March 25, 2014, Ray Walters <r...@solarray.com <mailto:r...@solarray.com>> wrote:
    OK everyone is steering me towards the Sunny Island.   I can
    probably justify the inverter cost difference to the customer,
    then I found the SMA Multicluster Box for the SI.  It seems like a
    glorified AC Combiner and transfer switch box, but it retails for
    over $20K! Yikes.
    Do we have to use that for a 3 phase install, or are there much
    lower cost alternatives.  This is out of the country and does not
    need to be NEC2014 compliant.  (maybe NEC 1956 compliant would be
    about in keeping with the rest of the wiring.......)  This would
    be a budget buster for sure.

    R.Ray Walters
    CTO, Solarray, Inc
    Nabcep Certified PV Installer,
    Licensed Master Electrician
    Solar Design Engineer
    303 505-8760

    On 3/25/2014 4:21 PM, Kevin Pegg wrote:

        Hi Ray,

        I have several 3-phase off-grid inverter/battery/generator
        systems out there.

        - SMA Sunny Island is the best. Can scale to at least 180 kW,
        maybe more. Reliable & very solid. I have several sites going
        over 2 years without a single second of power outage.
        - Xantrex XW. It can work in a 3-ph config, but it's not as
        stable system. We have taken to preventatively rebooting the
        systems every 4 months and that helps a lot - at least the
        outage can be planned and on our terms.
        - Outback has had so many power quality nightmares I won't go
        there anymore.
        - I believe Magnum has a 3-ph option but haven't installed one
        yet.

        SMA inverters are more expensive. And they work very well.
        They also have a very good battery charging algorithm and
        integral gen start control.

        Kevin

        -----Original Message-----
        From: re-wrenches-boun...@lists.re-wrenches.org
        [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Ray
        Walters
        Sent: March 24, 2014 6:44 PM
        To: RE-wrenches
        Subject: [RE-wrenches] 208 3 phase Off Grid Inverter


        Hi All;

        I'm exploring options for an off grid project with an existing
        30 Kw
        Kohler wired for 208 vac 3 phase.  The generator runs some 8
        hp air
        compressors, so rewiring it is not an option.  We're primarily
        interested in reducing gen run time from the current
        situation: 14 hrs/ day.
        So far, only the Outback VFX inverters seem capable of being
        wired in
        208, 3 phase, but according to the manual they can only be
        stacked 1
        inverter per leg. This limits the system to only 3 inverters
        total, or
        10.8 kW.  I would like expandability beyond this.
        1) are there any other inverters available that I'm over looking?
        2) Should I consider a transformer to convert from 208
        vac/3phase to 240
        vac/ singe phase?

        We're not going to even try to run the compressors, just the other
        single phase loads, mostly 120 vac, but we have a couple of
        small air
        conditioners, that are currently running on 208 single phase.
         I believe
        they would run fine on 240 vac, as they have a name plate
        rating at 230 vac.
        3) We may possibly run 2 separate 3 inverter stacks and only tie
        together at the battery, but otherwise they would not be
        connected. This
        seems inefficient, and would require some load balancing of
        the various
        inverters.

        All help and discussion is greatly appreciated as always,


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org