Do NOT connect chokes from any of the PV leads to ground.  It will create a DC 
path where no DC path should exist.  It's hazardous, and can/will destroy the 
inverter.

Inductance is indeed an offset to capacitance in many situations .. but this is 
not one of them.


Dan Lepinski

Professional Inverter Design Engineer (among many other things...)


--------------------------------------------
On Fri, 3/14/14, Chris Mason <cometenergysyst...@gmail.com> wrote:

 Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof
 To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
 Date: Friday, March 14, 2014, 9:07 AM
 
Typically when capacitance is a problem, the answer is inductance. Have you 
looked at adding some chokes between the DC negative and ground to counteract 
the capacitance?
 
 
 On Thu, Mar 13, 2014 at 10:31 PM, Marco Mangelsdorf <ma...@pvthawaii.com> 
wrote:
 
 Friends,
 
 We have run across an odd technical problem at our commercial install at a 
laundromat on our island.   Attached is the description of the issue from SMA.  
We don’t know much except that we are switch out the TL inverters to the old 
style US inverters because SMA has no fix for the phantom ground tripping.  The 
issue is beyond our feeble understanding.
 
Any observations to share?
 
Thanks,
 
marco
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to