Of course the objective in locating fuses is almost a catch-22. On the one
hand they should be as close as possible to the batteries, on the other hand
you can't locate the fuses in the same enclosure as the batteries as there
is a chance that if they were to open, the arcing may ignite any hydrogen
that is present.

We usually locate them immediately on the side of the box that the batteries
are in, inside a jbox.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of frenergy
Sent: Saturday, February 08, 2014 4:53 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC Fusing/Breakers for Battery Circuits

 

So help me out with a little more detail please.  Example (Dan's
configuration and my current in-progress install):  2 Strings of 8, L-16s
for 48V. nom.  Destination: the common pos bus at the bottom of a pair of
125 amp CBs as OCP for 2, VFX3648s.  

 

        Positive battery current path: from each end of both battery string
pos terminals, the next stop would be a (110 amp?) Class T fuse, one for
each cable/string.  Then cables from each of these fuses would land on one
Bus (hefty chunk of copper bar stock) mounted on inside of battery box
(backed up with Dan's cement board), combining the outputs of both batt
strings.  From this one bus, run 2 cables to the pos bus at the bottom of
the 2, 125 Amp CB's (in this case provided in the OB-DC Flex enclosure,
protecting the 3648s.

 

        A little simpler (better?) would be to just bolt the Class T fuses
right to the bus in the battery box, eliminating some cable.
Feedback?...and thanks,

 

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax

 

----- Original Message ----- 

From: Dan Fink <mailto:danbo...@gmail.com>  

To: Allan Sindelar <mailto:al...@positiveenergysolar.com>  ; RE-wrenches
<mailto:re-wrenches@lists.re-wrenches.org>  

Sent: Saturday, February 08, 2014 12:05 PM

Subject: Re: [RE-wrenches] DC Fusing/Breakers for Battery Circuits

 

Allan; 

It's a topic much on my mind recently and i will provide a writeup soon.
It's all very well documented. I do have photos, but they don't show the
fire damage to the wooden battery box unfortunately, the client was a bit
flustered getting all the batteries out of there after the incident and when
I showed up he had already demo-ed the box. But the photos of the batteries
themselves do tell the story rather well. 

There was another issue also.....his Xantrex power panel was wired with a
'self destruct switch' main battery cutoff. I did not design or install the
panel. But his logical reaction in seeing smoke coming out of his battery
box was to open the main battery disconnect breaker on the panel, which then
put solar 140vdc onto the inverters  inputs. Both were zorched by high
voltage. He should have opened the solar breaker first, then the main DC.
His homeowner's unsurance did cover most of it all.

The batteries were 8 years old....end of lifespan situation.

Lessons learned......OCP on parallel battery strings, and cement board liner
in all battery boxes, if they are field built wooden.




Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342

 

 

On Fri, Feb 7, 2014 at 10:36 AM, Allan Sindelar
<al...@positiveenergysolar.com> wrote:

Dan,
Do you have a writeup on that event? Any photos? I have many plywood battery
enclosures in the field.
Thanks, 


Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 <tel:505%20424-1112>  office 780-2738 cell
www.positiveenergysolar.com <http://www.positiveenergysolar.com/> 

 

On 2/7/2014 10:26 AM, Dan Fink wrote:

Does anyone have any elegant solutions to this? It's really time consuming
and ugly to run big parallel battery string wires *out* of the battery
enclosure to class T fuses, then back into the battery box. It looks very
ugly and DIY, and in conduit adds a few hundred to the install cost just for
labor. The Class T fuses and blocks themselves are not particularly
expensive. 

I have been recommending parallel fusing on battery banks of 2x8 L16s and
over now, after a nearly tragic incident with a bad cell that shorted. The
(perfectly legal) wooden battery box made the fire much worse. A pet peeve
of mine. 

 




Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342





_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

 

  _____  

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to