I think I just read that SMA has changed their long-standing 15A per string
fuses to 20A.

You might look to see if it applies to existing systems.

Hope it helps.

 

Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, February 06, 2014 12:50 PM
To: RE-wrenches
Subject: [RE-wrenches] DC Series Fusing in inverters

 

SMA inverters typically come with 15A KLKD fuses pre-installed. I have seen
a bunch of blown fuses recently (after cold weather)... It seems that some
dealers are just assuming the 15A fuse is okay for series strings and not
doing the calculations. I've been finding quite a few Evergreen systems or
parallel connected two-string SunPower systems that should have 20A fuses
per NEC 690.8. The problem does seem to be worse where inverters are exposed
to direct sunlight, presumably from fuses that no longer meet their ampacity
rating due to heat.

 

Anyone else run into this frequently?

 