You might want to try one of those lights up where the inverter is and see if it flickers up there when a load at the other
end is turned on...    Use walkie-talkies maybe ?

Are you sure it's not just surge regulation voltage response time of the inverter itself ?

boB



On 2/2/2014 4:01 PM, Chris Mason wrote:
You should rent or borrow a power quality analyzer to look at the phase angles and harmonic distortion throughout the day. A scope will also help to allow you to look at the waveform of the inverter produced electricity. You need to properly identify the cause of the problem before you invest in any equipment.

Resistive loads will not change phase angles. Only capacitive or inductive loads can do that. However, LEDs work fine in commercial installations where 0.8 power factors are common so I doubt that is your problem. It is more likely that badly formed waveforms cause switching issues for the LED's driver electronics. Filtering may help.

Line to Line capacitors are probably not going to help, but Line to Earth capacitors could act as a high pass filter to shunt noise to ground.



On Sun, Feb 2, 2014 at 4:39 PM, Troy Harvey <tahar...@heliocentric.org <mailto:tahar...@heliocentric.org>> wrote:



    We've got a PV system that has long lines from the inverters to
    the house (1000 ft or so). While the wires are properly sized
    (2x350MCMs), it inherently has a lot of inductance due to the
    line-length. What We are noticing is that dimmable LED lights
    flicker anytime a new load turned on, even if that load is purely
    resistive and the overall current draw is small (20 amps or so).
    What I "think" is happening is the LED dimmer circuits get their
    cue from phase delays, and that the inductance of the line length
    causes some phase jitter everytime a load is applied - thus
    causing flicker.

    Has anyone dealt with this issue successfully (other than
    switching to incandescent lights)? Would a static capacitor bank
    at the house do the trick, or do we need some type of active PFC?
    And if static did you have any issues with constant power draw
    from the capacitors?



    Troy Harvey
    ---------------------
    Heliocentric


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com <http://www.cometenergysystems.com>
Cell: 264.235.5670
Skype: netconcepts


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to