If only LED lamps on dimmers are flickering, suspect the dimmers, but this 
isn't yet certain.  This can be assessed by plugging one of the flickering LED 
bulbs into the same circuit, but use the bulb in a table lamp and plug into an 
AC outlet to bypass the dimmer.  Does the LED bulb still flicker?  If so, the 
dimmer can be exhonerated for now.  It also means you have more work to do... 

Another wrench suggested using an oscilloscope to evaluate the AC waveform.  
That was THE best recommendation, and  should be your #1 task.  It will 
immediately help to indicate the culpret.  The waveform should be perfectly 
sinusoidal.  Dimmers rely on a phase shift circuit to turn on the power to the 
load.  If the AC waveform is distorted, it can cause the dimmer to activate 
erratically, and turn on at different points in each cycle of the AC waveform 
.. leading to flickering.

Pay VERY careful attention to "hot" and "neutral".  You want the 'scope probe 
tip on the "hot" conductor; and the scope "ground" on neutral.  Make certain 
the scope is in the "Hi-Z" mode (some 'scopes have a 50 ohm setting in the 
probe or elsewhere.)  Measure carefully -- and use a "ground-buster" to isolate 
the 'scope.  (Ground-busters are those three-to-two AC socket adapters 
originally intended for use where the third-pin "ground" didn't exist, as in 
older homes.)  Pay careful attention to the cleanliness of the waveform AND the 
consistency of the amplitude.  Either or both out of spec can cause flickering.

LED bulbs are significant sources of "EMI". "EMI" = electromagnetic inteference 
.. aka "radio frequency interference" .. and can affect AM radio, FM radio, and 
other "receiving" devices up to some surprisingly high frequencies.  Remedial 
options are limited here .. and are a topic for a totally separate discussion.


Dan




--------------------------------------------
On Tue, 1/7/14, Chris Daum <ch...@oasismontana.com> wrote:

 Subject: Re: [RE-wrenches] Flickering LED lights on and Outback Dual 
7248VFXsystem
 To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>
 Date: Tuesday, January 7, 2014, 8:51 AM
 
 
We have a variety of LEDs, cheap, expensive, etcetera -- but no dimmers.  We 
have shown no sign of flickering in any of them off our Radian inverter.
 
Chris Daum
Oasis Montana Inc.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
toddc...@finestplanet.com
Sent: Monday, January 06, 2014 9:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Flickering LED lights on and Outback Dual 
7248VFXsystem

the only ones i have on a dimmer are in the bathroom and they flicker. being we 
are grid tied (GVFX-3648) and the grid is up, i suspect this is because of a 
bad dimmer/lamp combo.

anyone find the RFI from led lamps a problem? i have to shut all mine off when 
using the 2 meter ham rig.



todd


On Monday, January 6, 2014 7:56pm, "frenergy" <frene...@psln.com> said:

Another $.02....
I have 2, FX3524's and 35 KWhrs of HUP's behind them....just cleaned and 
torqued the terminals/cables.  I run 6-7 brands, sizes, styles of  LEDS and 
some of them of them flicker while, in my case, the convection oven is running. 
 It quickly pulses (~10-20 times/second) to maintain a temperature.  Fridge is 
DC. The less expensive off-brand LEDs flicker, the big name brands don't.
Bill
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to