I had to quit watching at noon, so I was disappointed to have missed the
theatrics. I just installed a system on my home to NEC 2008 as is followed
here. I have convinced a local plans reviewer that since it was removed in
NEC 2011, the building official should waive the 690.47(D) requirement for
rooftop systems. He specifically asked me if it would return in NEC 2014,
and if I am reading this right, the answer is definitely "no."

Since there was no aesthetically acceptable way to run the additional GEC
in my case and make it "as close as practicable (which is ambiguous
anyway), I cut it out immediately following inspection - something I would
NEVER recommend a customer do, of course. Nonetheless, I feel this was a
reasonable and acceptable move given that there are thousands of systems
out there inspected under NEC 2011 that have not additional grounding
electrode.

I will continue to listen with great interest...

Jason Szumlanski

Fafco Solar





On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico <
richard.l.rat...@valley.net> wrote:

>
> Mr. Holt explicitly stated his desire to create a groundswell of opinion to
> immediately eliminate this requirement of the code. Would it not be better
> to
> carefully think through and discuss the issue, in contrast to what was
> permitted
> on his "show"?
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to