Marco,


You might try http://pv-cables.com/ my contact there is Bryan. They sell
all kinds of PV wire, connectors, etc for good prices.



Do you have 1000 V TL inverters or just 600 V? If you are using 1000 V the
whole wiring game changes quite a bit.



Best,



August



Luminalt



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Marco Mangelsdorf
*Sent:* Friday, August 30, 2013 2:54 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] double-insulated PV wire



Note that this also assumes that the conductor whips from the modules ARE
ALSO double insulated if they’re to be used with TL inverters.  Some mods
have ‘em, some do not.



*From:* re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org<re-wrenches-boun...@lists.re-wrenches.org>]
*On Behalf Of *William Miller
*Sent:* Friday, August 30, 2013 11:52 AM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] double-insulated PV wire



Marco:





Good point.  If one can position transition boxes close enough to the
modules, you can use only the leads from the modules, avoiding the need to
buy any PV wire.  It is surprisingly easy to do.  See:



http://www.millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wiring/_PV_Cable_Wiring.html



WM





double-insulated wire has to be used from the module series string to the
first enclosure and enclosed raceway where the transition to standard
THHN/THWN wire can be made.



marco
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to