Hi Glenn,
I believe the answer to
your question is yes.
The SMA technical
report on off-grid supported inverters and issues is found at:
http://files.sma.de/dl/7910/SB-OffGrid-TI-US-en-15.pdf
Best,
Jeff
Glenn
Burt wrote:
Did they
mention if they support the shifting into/out of grid tied mode via the
SMA comms bus like the transformer based Sunny Boys do? Glenn
Allan-
SMA tech support confirmed with me yesterday that the 3/4/5 kW TL units
are compatible with the SMA frequency shifting.
On 2013/8/2
16:34, Allan Sindelar wrote: > Will the Sunny Island mate up with
these Sunny Boys that have the > limited backup capability during
an outage, as they will with standard > Sunny Boys? > Thank
you, Allan > > ------- Original Message -------- >
Subject: Re: [RE-wrenches] SMA Secure Power Supply > Date: Tue, 23
Jul 2013 23:16:23 -0600 > From: Orion Thornton
<onsiteenerg...@gmail.com> >
Reply-To: RE-wrenches
<re-wrenches@lists.re-wrenches.org> >
To: 'RE-wrenches'
<re-wrenches@lists.re-wrenches.org> > > >
Hi
Carl and All, > > This spring we had the opportunity to
install a 5000-TLUS inverter for a > client, as a pre-release
version. The inverter was commissioned on April > 1st and has
produced about 2.7 MWhs thus far. As mentioned, the secure >
power supply (SPS) requires a dedicated outlet with a switch to control
its > operation. For this installation we installed the SPS in
the mechanical > room, which is about 50 ft from where the
inverter is located. We chose the > mechanical room because it is
centrally located within the floor plan of the > home, making it
easily accessible to plug in emergency type loads, i.e. cell >
phone chargers, laptops, lamps, etc.. It is also very close to the
fridge, > which we plugged in with a short extension cord and
tested its operation in > the "stand-alone" mode (which is what
the inverter display when the grid is > down and the SPS in
activated). The inverter had no problem powering the > fridge.
The inverter display showed about 900 watts bypassed from the solar >
array to the SPS when the fridge cycled on....I must say it was a very
cool > feeling seeing this happen. > > As far as the
inverter itself goes, I only have a few minor complaints. > Like
the old SMA 1800U and 2500U, the conduit knockouts on the bottom of the >
inverter are at a slight angle, which means you must put a slight bend
in > your conduit. This is obviously a bit annoying and I can
only guess it has > something to do with the plug and play nature
of non-U.S. installation > techniques. The TLUS inverters are
also lacking Bluetooth communication, > unlike their HFUS
counterparts. I think this is a nice feature of the HFUS >
inverters and wish it was integrated into the TL's. > > With
no real difference in cost compared to traditional grid-direct >
inverters, I see no reason not to specify the TL, especially for someone
who > has a desire for "limited" power supply during a grid
outage. They can > always add a Sunny Island later on, if a more
robust backup system is > needed. > > I hope this
helps. > > Orion Thornton > Onsite Energy >
NABCEP Certified Solar PV Installer > > -----Original
Message----- > From:re-wrenches-boun...@lists.re-wrenches.org >
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of Jesse
Dahl > Sent: Tuesday, July 23, 2013 4:11 PM >
To:wire...@gmail.com;
RE-wrenches > Subject: Re: [RE-wrenches] SMA
Secure Power Supply > > I know the MREA in WI has one
installed on site, but not sure who installed > it. > >
Do they have a representative on the list? > > Jesse > >
Sent from my iPhone > > On Jul 22, 2013, at 6:18
PM,wire...@gmail.com
wrote: > >> If we have another long
outage here in CT and we seem to have one every > year now, I
don't want to have to explain to my customers why I didn't use >
this inverter. > > -- > > *Allan Sindelar* >
_Allan@positiveenergysolar.com_
<mailto:al...@positiveenergysolar.com> >
NABCEP Certified PV
Installation Professional > NABCEP Certified Technical Sales
Professional > New Mexico EE98J Journeyman Electrician >
Founder and Chief Technology Officer > *Positive Energy, Inc.*, a
Certified B Corporation^TM > 3209 Richards Lane > Santa Fe,
New Mexico 87507 > *505 424-1112 office 780-2738 cell* >
_www.positiveenergysolar.com_
<http://www.positiveenergysolar.com/> > > > >
_______________________________________________ > List sponsored
by Home Power magazine > > List Address:
RE-wrenches@lists.re-wrenches.org > >
Change email address
& settings: >
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > >
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > >
List rules & etiquette: > www.re-wrenches.org/etiquette.htm > >
Check out participant bios: > www.members.re-wrenches.org > _______________________________________________ List
sponsored by Home Power magazine
List Address:
RE-wrenches@lists.re-wrenches.org
Change
email address &
settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List
rules & etiquette: www.re-wrenches.org/etiquette.htm
Check
out participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
|