Drake

Keep the absorb rate recommended for the CC. The trimetric strays over time and 
will become accurate again when you overcharge (equalize)

The math:
Amp hours of battery @ 20 hour rate divided by max charge available in amps, 
from whatever you using to charge (solar or inverter/charger)
Times .42 = absorb time in hours 

i.e. your system 980 watts,  980 divided by 28.8 (average volts) = 34 amps max 
charge
370 AH divided by 34 = 10.88 X .42 = 4.57 round up to 4.6 hours absorb time for 
the CC
Your inverter VFX3524 max charge 85 amps... 370 divided by 85 = 4.35 X .42 = 
1.82 absorb time for the inverter/charger when running generator

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
Customer Service and Accounting 888-895-6810 
Grid tie sales 888-895-7847 
Off Grid sales 888-895-4058 
Other Product Sales 888-895-9612 
Central America Sales (Panama) 507-6-126-1253 
Shipping and Receiving 888-895-6497 
Tech Support 888-895-8179
SKYPE:  thesolarbiz

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Monday, July 22, 2013 10:04 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16s

Hi Larry,

I will bump up the absorb voltage to 29.6 V. How long do you think the bank 
should stay in absorb at that rate?  The bank now seems healthy, with the bad 
battery replaced.  It does accept charge, without going high prematurely.  The 
max charge rate from the array is around C/10. The system can also be fast 
charged from a Honda 6500 inverter generator through the Outback 3524 VFX.

We have a Trimetric meter on the system. The discrepancy between the percent 
charge and the voltage is what demonstrated that we had a problem.

Thanks,

Drake



At 09:30 PM 7/19/2013, you wrote:
>Hi Drake,
>
>It always concerns me when I hear that a battery bank reaches absorb 
>setting very quickly. It typically means one of two things: very few AH 
>were removed from the bank; the battery bank has sulfated cells due to 
>chronic undercharging. Far too often I find the latter to be true.
>
>Healthy batteries will accept current and hold the charge voltage down 
>with a fairly linear, slow climb to absorption voltage. Sulfated 
>batteries do not accept current well which allows voltage to climb 
>rapidly as the battery presents little load on the charging system. I'm 
>not sure how this plays into your original post about a bad cell but it 
>seemed worth mentioning.
>
>My opinion is to aggressively charge, by using higher voltage, large 
>flooded batteries. This is especially true when the PV system is 
>moderate or undersized. 29.6 volts is what Trojan recommends. You can 
>go as high as 32 volts on the L-16's but make sure the temperature 
>compensation is installed properly and working. You will use more water.
>
>One last comment, I highly recommend that ALL off grid systems have a 
>battery capacity monitor installed. It's kind of like flying an 
>airplane without a fuel gauge...it might not end in disaster.
>
>Larry Crutcher
>Starlight Solar Power Systems
>
>
>
>On Jul 18, 2013, at 1:11 PM, Drake
><drake.chamber...@redwoodalliance.org> wrote:
>
>Tom,
>
>The batteries usually reach absorb voltage shortly after the sun hits 
>the array. The reason the bank wasn't working correctly is that one 
>cell was dead in one of the batteries.
>
>I could increase the absorb time to 4.6 hours and the voltage to 29.6, 
>especially since the bank has a new battery. That is longer and higher 
>than I'd previously heard recommended.
>What would be the effect on water
>consumption?  How did you calculate the absorb time?
>
>Thanks,
>
>
>Drake
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to