Hi Jason,
That helps clarify the situation a little bit. I'm not familiar with the Lennox product. That said, Enphase M190 cabling has a line 1, line 2, and neutral (I believe blue colored) then you add a ground. The neutral and ground should not connect. That is consistent with what you said below in your recommendation. Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski *Sent:* Friday, July 05, 2013 4:25 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] EGC for Enphases I think what Dave is saying is that the enphase cable neutral is connected to the EGC in the roof mounted j-box, and no neutral is run to the Lennox panel or disconnect. While the neutral should not carry line current under normal operation, Enphase calls it a neutral - look up the NEC definition of neutral. I can see an AHJ having reservations about this, whether the "combined Neutral/EGC/GEC" is bare or insulated. I would not waste time trying to argue this with the AHJ. I would bring three current carrying conductors plus a combined EGC/GEC to the main distribution panel, just like every other Enphase job we do. I spend a fair amount of time explaining how this solar powered air conditioner is nothing revolutionary, except for the creative marketing. Anyone out there try to team up with a HVAC company to market any A/C unit as solar powered? Jason Szumlanski Fafco Solar On Jul 5, 2013 5:14 PM, "August Goers" <aug...@luminalt.com> wrote: Hi Dave, I'm not sure I'm understanding your scenario clearly but I'll take a crack at it. The Enphase system should have a bare #6 GEC for each micro and can then transition to a #8 green GEC once in conduit and run all the way back to the main ground electrode system. The #6 and #8 should be irreversibly crimped together since the GEC needs to be continuous. Certainly it is not okay for the neutral in the Lennox panel to be bare unless it is somehow a main panel. You could run the DC GEC along with the other conductors and it can serve as a dual purpose GEC and equipment grounding conductor per 2011 NEC 690.47(C)(3). Best, August -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click Sent: Wednesday, July 03, 2013 6:26 AM To: RE-wrenches Subject: [RE-wrenches] EGC for Enphases All, I was just looking at small 4-module Andalay (Enphase 190) system tying into one of the Lennox solar-ready air conditioners. The engineer had specified the 690.47(C) GEC be run directly from the array down to the existing electrode. Running from the inverters is a 2+G wire to the Lennox panel; they are using the uninsulated ground as the circuit neutral. It seems to me that this violates 200.7 (grounded conductor marked white or grey). Also, 250.134(B) (EGC run with circuit conductors), about which the engineer states "I have been studying the NEC on this and I believe that the intent is to permit the ground to be carried with the current carrying conductors, not require." Am I missing something? Thanks, Dave _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org