True, as mentioned 160 is not a standard size, but you also cannot use a 
smaller size for a load side connection, unless you can use/find equipment 
rated for continuous duty...then you'd only need a 125A OCPD.

Typos courtesy of my iPhone. 

On Jun 17, 2013, at 1:33 PM, Pekka Laine <pe...@photonsolarpower.com> wrote:

> Dear Fellow Wrenches,
> 
> We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, 
> each outputting max. 25A.  We are landing those into a dedicated load center 
> with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would 
> need a 160A breaker.  This also equals to the maximum we can backfeed into a 
> 800A/800A Main Service on the load side according to the "120%" rule.
> 
> The problem now is that we cannot locate any kind of 160A breaker or even a 
> 160A fuse for a AC disconnect.
> 
> Has anybody ever done this without doing a "line-side tap?" It is hard to 
> believe that there wouldn't be an existing solution to landing maximum PV 
> into a 800A service. Are we missing something?
> 
> Any good ideas or comments would be appreciated.
> 
> Sincerely,
> 
> Pekka Laine
> 
> President
> Photon Solar Power Inc.
> www.PhotonSolarPower.com
> Cell. 760-556-8170
> Toll Free 888-SUN-ACDC
> CA Lic. #933648
> NABCEP Certified PV Installer # 032611-174
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to