I found out that the appliance will work fine from an extension cord with a 
portable generator.
The appliance will not even work however when the backup gen is running and 
transfering through the inverters.
Outback T.S. suggested to check the Neutral to ground bond so that is the next 
step. Also tried to set the Power Save levels the same (stacked pair)

Jeremy
All Solar
  ----- Original Message ----- 
  From: Exeltech 
  To: RE-wrenches 
  Sent: Wednesday, April 17, 2013 1:51 PM
  Subject: Re: [RE-wrenches] Outback wave form


        Wrenches,

        While the addition of a capacitor may resolve issues associated with 
various
        inverter/appliance/motor combinations, please make sure the 
capacitor(s) get
        switched OUT of the circuit (disconnected) when the load itself is 
disconnected.

        Failure to do so could under some circumstances cause the inverter 
control-loop
        circuitry to go unstable, leading to unpredictable inverter operation, 
and possible
        damage/failure in the power system.  Disconnecting the capacitor with 
the load
        alleviate this possibility.


        Regards to all...


        Dan Lepinski



        --- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems 
<la...@starlightsolar.com> wrote:


          From: Larry Crutcher, Starlight Solar Power Systems 
<la...@starlightsolar.com>
          Subject: Re: [RE-wrenches] Outback wave form
          To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
          Date: Wednesday, April 17, 2013, 2:09 PM


          We experience issues like this from time to time. PF seems to be the 
culprit. Have you measured it or looked at the waveform yet?  How an inverter 
deals with PF seems to vary broadly. For example, the Splendide XC2100 
washer/dryer will not work on a Magnum Energy and a few other sine wave 
inverters. However,  it will run on a low cost GoPower or Samlex sine wave 
inverter. Below is a scope trace of voltage/current of the Magnum inverter & 
Splendide washer. Upper trace is voltage





          By adding a 50uF run capacitor inline, it somewhat tames the current 
phase and the sine wave so the Magnum can operate the washer. 




          (Special thanks to Al for the discovery and photos)

          Larry Crutcher
          Starlight Solar Power Systems


          On Apr 16, 2013, at 9:46 AM, All Solar <allso...@scswifi.net> wrote:

          Have a client with a new coffee maker that will not run from their 
new dual outback setup. Has anyone heard of this lately. We have had no 
problems with appliances and sine wave inverters. What to look for?

          Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
          _______________________________________________
          List sponsored by Home Power magazine

          List Address: RE-wrenches@lists.re-wrenches.org

          Change email address & settings:
          http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

          List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

          List rules & etiquette:
          www.re-wrenches.org/etiquette.htm

          Check out participant bios:
          www.members.re-wrenches.org





          -----Inline Attachment Follows-----


          _______________________________________________
          List sponsored by Home Power magazine

          List Address: RE-wrenches@lists.re-wrenches.org

          Change email address & settings:
          http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

          List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

          List rules & etiquette:
          www.re-wrenches.org/etiquette.htm

          Check out participant bios:
          www.members.re-wrenches.org

       



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to