Hello Wrench Team, Please forgive as this seasoned design engineer contributes to your discussion:
The conditions and symptoms as originally posted are: 1) A PV array consisting of four Solarworld SW165 PV modules. [72-cell, mono PV, Voc=44.1V, Vmpp=35.3V, Isc=5.2A, Impp=4.7A, all values at STC.] All four PV are parallel-connected. (See item #2 for substantiation.) 2) The PV terminate into a Blue Sky Energy 3024i [30A max out, with automatic current limiting]. V input max for this unit is specified to be 57 volts. This maximum voltage would be exceeded by just two of the above-mentioned PV connected in series. Subsequently, my contention the PV are connected in parallel is supported. 3) One of the PV modules has permanently dropped from ~30-35v output to 13v, regardless of test or operating conditions. 4) When the failed panel is removed from the array, the three remaining panels come back to normal voltage, but after approx 15 minutes drop down to around 13v on the Blue Sky display, even though the individual output from each panel when unhooked and tested in full sun show about 35v. 5) After turning the system off and on again a few minutes later the normal voltages return but drop again in about 15 min. The failed panel stays at 13v, does not recover. Speculative long-distance diagnostics are always challenging. First: The PV module that shows 13 volts open-circuit voltage under all test conditions (hot, cold, open-circuit, etc.) has experienced permanent failure (short) of two of the three bypass diodes. Explanation: Bypass diodes typically shunt 1/3 or 1/4 of the cells in a module. The specified PV have 72 cells, so there's one bypass diode across each of 24 cells in this particular PV module. When a diode fails, it shorts the portion of the module across which it's connected, and the PV voltage drops accordingly. Next: Ron Young (original poster), stated "the voltage of the remaining modules "drops" after 15 minutes use when the system is turned off, then back on again". Ron didn't specify the magnitude of this drop, so I can only guess whether this is the normal Voc to Vmpp decrease .. or he means this too is a decrease from nominal Voc to 13V or some similar voltage. Presuming the latter, this would indicate the heating of the PV is causing one or more bypass diodes in one or more of the remaining modules to fail short intermittently. To that, and to isolate the affected module, the PV must be disconnected from each other, and each module tested separately under the conditions under which the failures were noted. As a point of clarification, and since the four PV in this array are parallel connected, there is no appreciable current being forced through any one module by any of the other modules when all are operating normally. In the event of one or more shorted bypass diodes in a module, then all current from the remaining PV in the array will flow through the shorted diodes in the faulty PV. Defects in the cell buss structure or connections could come into play in a parallel array by causing hot-spot heating, along with possible current being forced through the PV due to the excessive voltage drop caused by that resistance. This could also cause the bypass diodes in the affected PV to be forced into the conductive mode. If this happened often enough, could in turn lead to eventual failure of the diodes, as many bypass diodes relied on convective and radiant cooling within the junction box - and this doesn't work very well. I've got thermograph images of junction boxes with bypass diodes conducting, and the measured temperatures are impressively high, and very eye-opening. That said... The only means to accurately diagnose the PV would be to completely disconnect them, face them into the sun, let them heat up, then at an absolute minimum, take Voc and Isc measurements for each module. It would also be highly recommended that the Isc measurement be taken for a period of several minutes, because internal heating (and subsequent failure of bad connections) may not show up until the connection(s) gets hot enough to fail. Also ... To correct an earlier statement made within this thread, where a poster said diodes usually fail "open" ... this is incorrect. Diodes fail short. The only time they fail "open" is when they are mechanically faulty, which then causes the conductive path to open (rare), or when they are totally destroyed -- and thus obviously open. Can a diode fault be "intermittent"? Yes. Though not common, it is always mechanical in nature caused by thermally-related expansion/contraction. Otherwise, "short" is the failure mode in diodes. Conclusions: One of the four PV has suffered permanent failure in two of the three bypass diodes. Symptoms reported by Ron Young (the original poster) indicate one or more of the remaining PV are experiencing intermittent thermally-related short-circuit failures in the bypass diodes, which then decreases the output voltage after ~15 minutes as Ron reported. When the PV cool, the thermally-induced short in the diode(s) goes away, and the PV output voltage returns to normal. Remedy: Depends on the accessibility of the bypass diodes. If the diodes and junction boxes are potted or otherwise rendered inaccessible, then replacement of the affected PV is indicated. If all four came from the same production batch, I'd recommend changing out all of them, even if still functioning normally. Solarworld would be responsible only for those PV that are malfunctioning -- not for any normally operating product. Option: I'm not personally acquainted with this specific PV, but if its vintage is such that the diodes themselves are accessible and replaceable (some in older models of PV were), then replacement of the diodes would be a consideration, rather than the entire PV. If this is the case, ensure the diodes are more robust than the parts used in the original product, and that all connections to the new parts are solid. Regards to all, Dan Lepinski 41 years in solar energy ... --- On Sun, 5/12/13, d...@energysolarnow.com <d...@energysolarnow.com> wrote: From: d...@energysolarnow.com <d...@energysolarnow.com> Subject: Re: [RE-wrenches] not sure what's going on here To: re-wrenches@lists.re-wrenches.org Date: Sunday, May 12, 2013, 12:22 AM Ron et al- The firmware in the controller sounds likely, but a faulty shorted bypass diode does not. Isn't that what bypass diodes are supposed to do -- turn on and short (bypass) a shaded row of cells? We use to see this half-panel voltage as a failure mode with the old Kyocera 120's when they were still blue. The solder mask fails in a hot spot and opens, so no current can flow in that row of cells. Then the bypass diode is just doing it's job by bypassing current at lower module voltage, just as it does when half the module is shaded. If there are other modules in parallel they will push current into the reduced-voltage one until they are also at reduced voltage, which is sensed by the controller. Sounds like a lot of current is being pushed through the damaged module, which will fry the hard-working bypass diode(s) or the solder mask wire in that low module. Best to disconnect the low module or the others will kill it. I cannot think of any physical way the rest of the solar modules can work at full voltage for awhile without the damaged one, then have the voltage drop suddenly under load, only to be seen at full voltage again when disconnected. Do I have this sequence right? -- This sounds like software (or firmware) attempting to do MPPT in the controller. If it is faulty firmware as Larry C. wrote then it should be upgraded. So, could the controller be complicit in damaging the low module? Hmmm.... Don Barch Energy Solar _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org