David, 

Since a PV module is a constant current device, I don't believe this will take 
place. For a given amount of light (plus all factors affecting power), the 
current potential will be there. What force can act upon the current to reduce 
it? Consequently, the lowest Vmp the inverter can track will dictate the 
voltage for all strings. This means less power from the highest Vmp modules. Do 
you agree?

Larry Crutcher






On Apr 28, 2013, at 9:33 AM, David Katz <dk...@aeesolar.com> wrote:

Kirk
The 43volt 5.5 amp panel will operate at 3.6 amps, so it's voltage will move up 
toward open circuit voltage, raising the mppt voltage of that string.  I would 
bet that the voltage of that entire string will rise to match the higher 
voltage string by moving toward open circuit voltage.  It should work fine.
David Katz

Sent from my iPhone

On Apr 28, 2013, at 9:01 AM, "Kirk Herander" <k...@vtsolar.com> wrote:

> Hello everyone,
>  
> I am at present adding to a -20- panel array of old Sanyo HIT “lipped” 200 
> watt panels. They are configured in -4- series strings of -5- panels, with a 
> string MPP voltage of 279 vdc (55.8 v, 3.6 a each). The customer wants to add 
> another nominal 2 kw using the (now) Panasonic 235 watt HIT’s which have an 
> MPP of 43.0 vdc, 5.5 a. I am locked in to an existing SMA 6000US inverter. 
> Obviously I cannot get all the strings to the same voltage. But I can get 
> relatively close by rewiring:
>  
> String 1: -7- 200 watt @ 55.8 ea. = 390.6 v MPP
> String 2: same as string 1
> String 3: -6- 200 watt @ 55.8 plus -1- 235 watt @ 43.0 = 377.8 v MPP
> String 4: -9- 235 watt @ 43.0 = 387 v MPP
>  
> Under this scenario there is a delta of about 12 vdc between high and low 
> MPP. I assume the entire array will operate at the 377.8 V MPP. I know that 
> the 235 watt panel will be current limited also in string 3. Am I missing 
> anything obvious in doing it like this? How will the inverter arrive at an 
> operational MPP voltage?
>  
> PS. In a pinch I could install a leftover 200 watt HIT I have in the shop. 
> That way I could have -3- strings of -7- 200’s @ 390.6 v MPP, and one string 
> of 235’s @ 387v MPP. But I would prefer not to use this panel since the frame 
> is damaged.
>  
> Kirk Herander
> VT Solar, LLC
> dba Vermont Solar Engineering
> NABCEPTM Certified Inaugural Certificant
> NYSERDA-eligible Installer
> VT RE Incentive Program Partner
> 802.863.1202
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to