We installed 2 of the original SI4248s back in 2006. The installation manual
specifically noted that the units had a "Built in DC disconnect" though and
not a circuit breaker. There is no mention of interrupt current.

Instructions also said to "Ensure that an approved DC disconnect and
over-current protection is installed between the batteries and inverter."

Both have worked flawlessly since then except that in 2011 one of the
"disconnects" developed a bad connection and arced when turning the unit on.


 

 

Jim Duncan

North Texas Renewable Energy Inc

www.ntrei.com <http://www.ntrei.com/>  

NABCEP PV 031310-57

TECL-27398

nt...@1scom.net 

817.917.0527

NABCEP Logo

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Wednesday, April 10, 2013 7:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

 

boB,

SMA does recommend protecting Sunny Islands with a fuse on the battery, even
though the breakers on the units are rated for 10,000 Amps.  Are the  SI
breakers inferior others you have mentioned? 

Thanks,

Drake



At 12:14 AM 4/10/2013, you wrote:




After 100's of thousands of  inverters having been shipped in the last many
years
and thousands of inverters broken and shorting the battery terminals, there
has
never been (to our knowledge) one breaker that has not tripped.

The Midnite site lists the AIC rating of all our breakers I believe.

The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...

http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%2
6_COS_0.pdf 

I guess there isn't a graph of AIC vs. voltage on their F series web page
but we remember
them showing us figures or a graph that says those breakers have an AIC of
more than
100,000 amps at 48 volts.  We'll try to find that info or you may be able to
get that
from Carling.

I have, many times, directly connected these breakers across good L-16
battery strings
to demonstrate the left-hand rule to people where the 4/0 cable jumps apart
or towards each
other when very high current passes through those wires when they are near
each other.

It always trips.  Never tried it at anything above a 48V battery banks IIRC.

Robin would like to mention that anyone that wants to use T-Classc fuses....
Welcome back to the 1990's

boB


On 4/9/2013 1:23 PM, Ray Walters wrote:



Hey Bob;

Can you share that AIC vs Voltage chart?

Thanks,

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/9/2013 1:46 PM, boB wrote:




Those 250 amp and 175 amp breakers we have used for many many years now
have an AIC of 50,000 amps at 125 volts and if you look at the curve, at 48
volts
they are around 100,000 amps.  I think that this information is on the label
of the breaker.

How many problems have you had with the Carlings or any other type of
those large breakers ?

boB


On 4/9/2013 10:40 AM, Michael Welch wrote:



If anyone would like an Acrobat version of this article, you can find it
here:

ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf

William Dorsett wrote at 07:00 AM 4/9/2013:
 



This topic comes up often enough that we ought to mention a yellowed article
in Home Power, (1992 Issue 27, pg 26). Christopher Freitas wrote Overcurrent
Protection for Battery-Powered Systems where he describes experiments he did
back when he was with Ananda. He put a 2000 A Big Switch to initiate a short
(4/0 cable) between the terminals on a set of four golf cart batteries (2
strings @ 12V). In series, he put in a 500A Shunt so he could measure
current passing and various fuses and breakers. "For comparison, we decided
to directly short the battery.the meter read 6960 amps peak current (three
seconds) .during each test the 4/0 cable lifted off the ground 4 inches into
the air by the forces generated by the extremely high current.." They
videoed the 250 A ANN buss fuses arc and smoke; the 200A Heinemann Series AM
breakers (paralleled ones that maybe Roy mentioned) went 3 seconds without
breaking and the video showed a flash and blue smoke. 
175A ITE breaker with 42,000 AIC "simply tripped.but still allowed a peak
current of 2960 amps
200A Class T Littlefuse "opened promptly with no external signs of
stress.1920 amps peak current"
Christopher's recommendations: 
"Every AE system must have overcurrent protection able to interrupt the
maximum current available from the batteries. For most systems, the main
protection should use current limiting high AIC fuses, such as a Class T or
Class R. A disconnect switch which allows the fuse to be safely changed
should be included. A lower cost alternative is to mount the fuse in a fuse
holder without a disconnect. Although the fuse would always be electrically
hot,  it normally would not be changed during the life of the system. The
fuse holder should be mounted outside the battery enclosure. Fuses should
not be bolted directly onto the battery terminal, as they are not designed
to handle the physical stresses that can occur without the protection of a
fuse holder.
 
Fuses which have exposed elements, such as ANN fuses, should not be used
because they are not current limiting and have only 2500 amps AIC. They also
may be a significant hazard when installed near batteries. 
 
High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @ 65VDC)
can provide overcurrent protection for individual items. They cannot be used
to protect lower AIC breakers. This eliminates their use as a main
disconnect in most systems. 
 
Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or the
Square-D QO (5000A @ 125 VDC) can be used in load distribution centers and
components, but must be protected by a current limiting fuse. Using low-AIC
breakers alone will not provide sufficient protection with a battery system
and may be a significant hazard during short circuit situations."
 
It won't pull up anymore on HP's article search but probably Michael has a
copy he could post for those interested. 
 
Bill  Dorsett

 






_______________________________________________
List sponsored by Home Power magazine
 
List Address:
 <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
 <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> 
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
 <http://www.members.re-wrenches.org> 
www.members.re-wrenches.org
 






_______________________________________________
List sponsored by Home Power magazine
 
List Address:
 <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
 <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> 
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
 <http://www.members.re-wrenches.org> 
www.members.re-wrenches.org
 


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 

<<image001.jpg>>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to