Larry,

Thanks for your reply. For some reason the schematic I received from the tech 
at Atkinson did not show any wires being connected to pins 9 & 10 and as I'm a 
literalist I did not make those connections. After I received your (and other) 
feedback I connected gen power to those pins and the AGS seemed to function 
fine. Within 2 days the customer called me back saying his genny was shutting 
off after 20 mins of runtime. I told him to disconnect or reprogram one system 
component at a time to find the fault source. Before a fault source was 
determined, he observed that two batteries in his bank were experiencing the 
"battery terminals melting into the battery casing" (as was texted to me by the 
customer). I have no idea how a GSCM interface would cause or allow an 
overcurrent fault at the batteries but the timing of the installation seems to 
indicate that the AGS is at fault. Ever heard of this before?

Eric Stikes
SunHarvest Solar

----- Original Message ----- 
  From: Larry Crutcher,Starlight Solar Power Systems 
  To: RE-wrenches 
  Sent: Friday, March 01, 2013 11:48 AM
  Subject: Re: [RE-wrenches] GSCM-mini with Honda EM5000SX


  You need the line and neutral from the generator connected to pin 9 & 10 or 
the GSCM does not know if the generator is running or not.



  Larry Crutcher
  Starlight Solar Power Systems





  On Mar 1, 2013, at 10:30 AM, SunHarvest wrote:


  I've installed a GSCM-mini (interfaced with a Honda EM500SX w/manual remote 
start box) according to the attached schematic provided by Mr. Kendall of 
Atkinson. The unit is not functioning properly. It seems that the GSCM-mini is 
not recognizing that the generator is running.

  Here are the results of my troubleshooting:

  Start LED (yellow) on GSCM-mini blinks once every 5 seconds to indicate it is 
ready.

  When starting the generator using the MATE3 from either the manual Generator 
Status Menu, or using the auto 2 minute Voltage Start - 
  Generator starts OK, MATE enters RUN mode, no faults listed on MATE, AC IN 
shows USE AGS, i.e., everything looks OK. But when I press the OFF button on 
the Gen Status screen the STATUS goes to OFF but the generator will not shut 
off...until...

  At the time of manual start the GSCM begins going through the cycle of trying 
to start the genny then goes into a Lockout Fault Condition:
  Start LED goes to solid yellow, K1 light comes on, generator starts, K1 light 
goes off for 40 seconds, yellow Start light is solid, K1 comes back on for 20 
seconds, cycle repeats 3 times, K2 light comes on for 5 seconds, Gen Hz LED 
Fault blinks twice repeatedly, Fault LED (terminal 12) comes on solid, GSCM 
enters (Max Crank) Lockout Fault, ...then the generator shuts off.

  Seems the GSCM is not registering a Valid Run Condition. So, either the 
schematic for the 4000SX is not applicable for the 5000SX or the red wire I 
connected to terminal 8 (as shown in the schematic, needs to actually go to 
terminals 9&10, or I need to run a wire from the Pilot LED on the manual remote 
start box to terminal 8 on the GSCM...

  Any experience with this scenario?

  Thanksalot,


  Eric Stikes
  SunHarvest Solar
    ----- Original Message -----
    From: Chris Mason
    To: RE-wrenches
    Sent: Wednesday, February 20, 2013 6:26 PM
    Subject: Re: [RE-wrenches] Solar-direct pool pumping


    We install solar pool pumps quite frequently here in the Caribbean. We use 
Sunpumps - excellent company, great support. Email Joe Lines j...@sunpumps.com 
for design assistance, he is very helpful.



    On Wed, Feb 20, 2013 at 1:02 PM, William Korthof <wkort...@gmail.com> wrote:

      A few questions. 

      I have a customer who really wants a solar-direct pool pump for his home. 
Medium size in-ground pool and I'd like the pump to be strong enough to lift to 
the solar pool panels (12 ft lift above pool level). I'd like to offer him 
hardware that is at least one notch above experimental beta-test. I remember 
the SunCentric from several years ago, but not sure how durable that turned 
out, and I was having trouble a vendor for it now. Any suggestions for today 
with some favorable track record? Or suggestions on what to avoid? 

      William Korthof
      Sustainable Solutions Partners


      _______________________________________________
      List sponsored by Home Power magazine

      List Address: RE-wrenches@lists.re-wrenches.org

      Options & settings:
      http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

      List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

      List rules & etiquette:
      www.re-wrenches.org/etiquette.htm

      Check out participant bios:
      www.members.re-wrenches.org








    -- 
    Chris Mason
    President, Comet Systems Ltd
    www.cometenergysystems.com
    Cell: 264.235.5670
    Skype: netconcepts



----------------------------------------------------------------------------



    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm

    Check out participant bios:
    www.members.re-wrenches.org


  <EM4000SX_MINI-01.PDF>_______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org






------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to