Jeffrey,

I agree. We do structural analysis on every roof design and factor in the point 
loading at the attachment points. I had floated this idea because it came from 
an SE that I work with that also has a PV system. His theory is the definition 
snow loads are accumulation of snow over time. And most of the time snow will 
slide off the panels in 3-4 days. The panels would have to be placed so the 
snow would completely slide off the roof. I wanted to see what others thought 
of this approach who have been doing structural analysis. I appreciate your 
responses.

Gary


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of JRQ
Sent: Thursday, February 21, 2013 8:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Snow loads

Gary,

The snow loads that structural engineers design to are a worst-case scenario. 
It is true that snow tends to slough off of PV arrays quicker than your normal 
roof. However, if there is a major snow event, especially if it starts at night 
(this recent blizzard on the East Coast would be a good example), snow will 
build up on the array the same as it does everywhere else.

In many cases, a PV array actually makes the engineering assumptions worst. Any 
snow that lands on the modules transfers down to the attachments, and 
point-load the structural members. The weight of the snow is less distributed 
when it sits on a PV array, placing additional stress on individual members. I 
work in Massachusetts currently, and we often have to perform rafter upgrades 
to roofs that are fine otherwise for exactly this reason.

If you have any snow load requirements in your area, I would highly recommend 
you have a structural engineer review the structure, even if a structural stamp 
is not required.

Jeffrey Quackenbush


________________________________
From: Bob-O Schultze 
<bo...@electronconnection.com<mailto:bo...@electronconnection.com>>
To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Sent: Tuesday, February 19, 2013 3:00 PM
Subject: Re: [RE-wrenches] Snow loads

I would certainly agree with Will here. You can't make that argument as stated, 
it's wrong. Please don't try to make it to your AHJ, you take the chance of 
f-ing it up for everyone around there. I think the best argument you can try 
is:  aside from the usual 3-4lbs/sq/ft that the array itself ads to the roof 
load, snow will be very unlikely to build up on the modules to the degree that 
it builds up anywhere else on the roof. The freezing-rain-before-a-snow 
phenomena is very real and it WILL happen sooner or later. Not often perhaps 
and under most conditions the snow will leave the modules before the roof. 
But...Gotta be real about that.
Bob-O Schultze


On Feb 19, 2013, at 11:06 AM, Will White wrote:


Most structural engineers I’ve seen take a reduction for slippery surface but I 
think you’d be stretching things to say adding PV panels reduces the load to 
zero.  I have a 45 degree pitch roof and I get snow build up some times 
especially if we get freezing rain before the snow.

Also if you have an asphalt shingle roof you can create an unbalanced load with 
snow sliding off the south side and sticking on the north side.  Most engineers 
take this into consideration too.

Thanks,
Will

__________________________________________________________________________________________
Will White
Regional Field Operations Manager – New England

Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com<http://www.realgoodssolar.com/>





From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Gary Bassett
Sent: Tuesday, February 19, 2013 1:48 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Snow loads

Has anyone in the snow belt areas have any luck with convincing their local 
building inspectors that the snow melts or slides from panels, much like a 
metal roof only better. Thus your snow load would be reduced to zero where the 
panels have been installed.

Gary


_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


_______________________________________________
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



--
This message has been scanned for viruses and
dangerous content by Hudson Valley Computer 
Services<http://www.hvcomputerservices.com/>, and is
believed to be clean.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to