This is going back several years...
The Outback VFX series lacks the tight input current regulation of the SW series, so the max AC amps in is really just a suggestion. In many cases (and especially with these small generators) we want to set the max amps in as high as possible to minimize charging time and maximize C/rate. Yet a surge load can momentarily exceed the max amps setting. I have observed that the Honda inverter/generators have a quite sensitive AC output breaker, that will sometimes trip if a surge load (such as a refrigerator) comes on during a charge cycle set close to the generator's capacity. This incident was specific to a Honda 3000i. In contrast, Yamaha's EF3000iSE will lug when overloaded - not good for the generator, but also not likely to trip the output breaker. This is a different issue than was being discussed, but fits your question. Allan
Allan Sindelar
On 1/29/2013 3:42 PM, Greg Egan wrote:al...@positiveenergysolar.com NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder and Chief Technology Officer Positive Energy, Inc. 3209 Richards Lane (note new address) Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com
|
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org