I have two issuesyou should be consider before deciding to use the SolaDeck Models 0760-41AD and 0766-41AD:

1. The Temperature De-Rating of the existing ABB breakers sold by SolaDeck could cause high temperature "nuisance trips", particularly on maximum sized AC strings of 17 Enphase micro-inverters. If a high(er) temperature rated circuit breaker is not available from ABB, a prudent design would reduce the maximum number of micro-inverters in an AC string to 12.

   _Manufacturer_:  ABB 20A 2-pole din-mounted circuit breaker

   _Terminal Temp Rating_: 75C / 167F

   _Reference Temperature_: 20C / 68F

   _Ambient Temp Derating_:
   30C/86F = 18.7A
   40C/104F = 17.3A
   50C/122F = 15.8A
   60C/140F = 14.1A
   70C/158F = 12.2A

2. Another issue, at least in some jurisdictions, is the requirement for a roof-top AC Disconnect for micro-inverter systems. The SolaDeck, when used as an AC SCCB, may not meet the NEC Article 100 definition for "readily accessible" because a tool is required to open it.


Regards, Gary


On 1/3/2013 7:44 AM, Jason Szumlanski wrote:
SolaDeck Models 0760-41AD and 0766-41AD are rated for up to 60A at 240Vac.

Give them a call - Steve is very helpful.

*Jason Szumlanski*//

/Fafco Solar
/


On Wed, Jan 2, 2013 at 11:57 PM, Jesse Dahl <dahlso...@gmail.com <mailto:dahlso...@gmail.com>> wrote:

    I find info about the AC soladeck in my distributors catalog, but
    I don't find any information about it on Soladeck's website.




    On Wed, Jan 2, 2013 at 7:18 PM, Jesse Dahl <dahlso...@gmail.com
    <mailto:dahlso...@gmail.com>> wrote:

        Hello,

        I am in the process of installing a Enphase system that
        requires center feeding the individual 15 modules circuits. I
        am wondering about wiring the J-Box.  I need to cut all of the
        boxes into the center of the runs of Engauge cable and
        maintain the 6" of free conductor.  To do this, I will need to
        pull the trunk cable towards the J-Box.  There are a few spots
        where doing this may pull the inverter connection points to
        far from the inverter.  It looks like like the spots where
        this will be a problem is where the circuit of modules is made
        up of modules from different North-South rows of racking. I
        took some rough measurements at the end of the day,
        but haven't really laid the cable out to check if it will
        really be problem.

        I'm sure this is common, and easily fixed, but a conformation
        from another installer would surely be welcome.

        Thanks,

        Jesse







_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to