Jeff:

There is a code passage that specifically states that one does not need to provide full rated ampacity to a service. I am sure you can find it.

Find a way to prove, mathematically, that the system planned will provide adequate power. Create or find a spreadsheet listing all appliances and wattages and system watt hours provided. Dress it up, put your logo on it and sell it to the building department.

William Miller




At 07:52 PM 12/11/2012, you wrote:
Content-Type: multipart/alternative;
        boundary="----=_NextPart_000_0006_01CDD7F2.373D3CB0"
Content-Language: en-us

We have a client that just had assembled on his rural property a pre-fab modular home with "normal" wiring and 200 amp main panel and meter base. However, landowners around his property will not grant access for electric utility to cross and he needs to move in ASAP. He realizes that some day he should be able to resolve this utility access but until then he wants us to do an off-grid "basic" solar system with generator backup so he can at least power lights, well pump, and basic appliances. His budget will not allow a fully off-grid solar system so we wanted to do reduced solar and battery system with larger generator to fill in on bad solar days. He does have good solar exposure and lots of cleared land, but figures one day the solar and generator will become a backup system to a future grid connection so does not want to spend any more than absolutely necessary.

However ,this local inspector for this rural county has no experience with solar and is expecting to see a 200 amp service connection from the utility before allowing occupancy. He did hint that a 100 amp service connection may be allowed but nothing less. I know NEC does mention that a panel does not have to be supplied with the amount of service capacity it is rated for, but what other code issues can I point out to get this accepted without getting into a pis----- contest?

Thanks,

Jeff Yago

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to