Wrenches,Has anyone dealt with an issue with the Outback GVFX inverters where 
the Mate (status>fx>meter) will show the "AC in voltage" rising and falling 
between ~121V and 132V while a mulit-meter held on the inverter terminals shows 
the voltage is actually holding steady? When the mate/inverter shows the 
voltage hitting about 131V the inverter shows a red error light (AC in voltage 
to high) and i believe this is preventing HBX mode from working properly, such 
that the HBX setting will not trigger the grid to take over and allow the 
batteries to drain to the Low-batt cut-out. 
This issue only seems to appear when in "SellRE" or "HBX" mode, not when simply 
using the grid as 'passing thru'.
I have confirmed that there are no loose neutrals and that there is only one 
neutral to ground connection.
thanks,benn