Friends:

Keep in mind that Mac asked us about application of a specific section of the NEC, not if the rule makes any sense.

William Miller


At 05:32 AM 9/28/2012, you wrote:
Are you sure you can't? Since the bus has a rating of 150 A and is protected by a 100 A breaker, there is plenty of room to not over amp the bus from the two sources of power.

The amperage from the inverter will cancel amperage coming from the utility in the feeder. The wire will never supply over the 100 A. The theoretical max the inverter could backfeed would be 40 Amps in the 100 Amp cable if no loads were being supplied. It would certainly not be a safety issue. Am I missing something in the code?

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to