690.13 specifically states that the grounded conductor shall NOT be
disconnected. All sections of Chapter III (Disconecting Means) of Article
690 specifically refers to the ungrounded conductor.

Jason Szumlanski
Fafco Solar


On Fri, Sep 14, 2012 at 7:39 PM, Bob Clark <bcl...@solar-wind.us> wrote:

> Wrenches:****
>
> ** **
>
> A local utility person has suggested that both the positive and negative
> conductors from a solar array should be disconnected.****
>
> ** **
>
> Disconnect both or not?  2008 NEC supporting citation please.****
>
> ** **
>
> Thanks for your response.****
>
> ** **
>
> *Bob Clark*
>
> *SolarWind Energy Systems, LLC*
>
> *P.O. Box 1234*
>
> *Okanogan, WA 98840*
>
> *(509) 826-1259*
>
> * *
>
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
>
> [image: cid:822514723@19022009-0502]****
>
> * *
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to