Rich,

In your example you have 8kW feeding a 20kWh battery (assuming 400AH bat). This 
is about 0.4C charge rate. If these were flooded batteries, I might consider 
limiting bulk current to 0.2C because in standby use they do not need to be 
fully recharged in one day. Slow battery charging promotes longer life.

Since you mention that these are AGM I would not worry about the excess 
current, especially in a stand by configuration. Some AGM manufacturers publish 
that you can provide charge current up to 5C without harm. For your bank that 
would be 2000 amps at 57Vdc! I believe all good quality AGM's can withstand 
high bulk charge currents because of the efficient way hydrogen and oxygen are 
recombined. Controlling voltage is the more important factor. So I don't think 
you are missing anything.

Larry Crutcher
Starlight Solar Power Systems




On Sep 1, 2012, at 6:35 AM, Rich Nicol wrote:

Wrenches,
I’m have a mental block with battery backup systems such as the Outback Radian. 
Perhaps someone can help me get over it!
Essentially these systems sell back power off the top of the battery bank and 
the array is maintaining the state of charge of the battery bank through 
traditional charge controllers. If you have a modest battery bank sized for 
limited use on critical circuits and a good size array for the benefit of net 
metering I would think it would be necessary to limit the current the charge 
controllers are capable of delivering to the battery bank to prevent damage to 
the batteries when the controllers are Bulking or Absorbing, but then it would 
seem that we limiting the utility of the larger array. If the current from the 
controllers was not limited they will self-limit as voltage rises, plus I 
suppose they will mostly be in float mode except when the batteries are cycled 
but again it seems that we are limiting the capability of the array compared to 
a straight grid tied system with a traditional grid tied only inverter.
An example would be a 8000 watt array using a couple of flexmax80 controllers 
with a string of 8 - L16 AGMs feeding a  Radian.
What am I missing here?
Thanks
Rich
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to