Wrenches, 
This is baffling me and I need others experience. It is a small stand alone 
system with 4 L16s in series/parallel. Charging source is 2 Kyocera 140 watt 
modules. It is powering a satellite receiver as well as providing 120 VAC for a 
boat dock using a listed 3000 watt mod sine inverter. The inverter operating 
range is 10.5-15VDC. The Morningstar controllers are running the voltage up to 
15.6 in bulk and float.
At first it had two 10 amp controllers and I wondered if there could be a PWM 
situation existing. Swapping for a Morningstar SS20L gave exactly the same 
voltages. I replaced that controller with a MorningstarSL20 with no change in 
voltages to the batteries. I have used two meters as well as had the inverter 
tone the high voltage condition. I can shut off the solar input and get the 
batteries below 15 volts in a few seconds and bring the inverter online. I have 
repeatedly pulled surface charge off the batteries and watched the same 
voltages repeat themselves. I wondered about RF noise from the satellite feed 
messing with the PWM but unhooking it from the load side of the controller 
changed nothing. Batteries are gassing but not boiling out with no indication 
of a bad cell. In desperation I installed the spade jumper to switch the 
controller over to AGM settings and immediately saw the bulk and float voltages 
fall to the settings Morningstar lists in their
 manual.
It was 100 degrees when I was onsite last week so this is not a cold weather 
situation. Anyone have any thoughts as to what is going on here? I am 140 miles 
from the site and this will be my third trip to sort this situation out.
Thanks,
Nathan Jones
Power Source Solar
Springfield, MO
417-827-0738
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to