No. End Absorb Amps will only look at the controller current, not net battery 
current. If loads are on, the current may be higher than your setting and the 
controller will continue with monitoring the ChgT. More importantly, if current 
drops below your setting and the battery is not 100%, it will still drop to 
float mode. Not good. 

Without a FlexnetDC and Mate to determine SoC, the only use I can see for this 
function is if you had a constant load on the system. Then you could calculate 
the right transition value.

Larry 


On Jul 8, 2012, at 10:00 AM, mac Lewis wrote:

Larry,

Would the  Absorb End Amps setting act similarly to the IPN chargers from Solar 
Boost if you set a very long absorb time and had it end absorb stage after it 
dropped below the desired current level?

Thanks

On Sun, Jul 8, 2012 at 9:40 AM, Larry Crutcher, Starlight Solar Power Systems 
<la...@starlightsolar.com> wrote:
Hello Mick,

I think your set-points for voltage are fine. The Rebulk is of little 
importance for an unoccupied property as voltage should be easily maintained.

The bad news: In a nut shell you have told the MX charger to stop charging if 
the PV current drops below 45 amps or 0 to 60 minutes after reaching the absorb 
setting. I don't think you can ever reach 100% SoC with this setup so the 
battery may have been deficit charged every day.

Absorb Time Limit, Min:
With AGM batteries, this setting should be determined by measuring how much 
absorb time it takes for the current to the battery to drop below 0.5% of the 
banks rated capacity. For example, a 1000 AH bank this would be 5 amps. If it 
takes 60 minutes to reach this point, use that number for "Min". By leaving it 
at 0, the MX60 will choose the absorb time based on the bulk/absorb charge 
timer which may not be enough at an unoccupied property. Example, if the bulk 
time is only 30 minutes, the absorb time is 30 minutes unless the "Min" is set 
higher.

Absorb Time Limit, Max:
The factory default is 2 hours. This value needs to be at least 10 minutes 
longer than the "Min" time set above. One hour means that is the longest time 
the controller will stay in absorb.

Absorb End Amps (misc settings)
Here's the real culprit. By setting this at 45 amps, you have told the 
controller to stop absorb charging 15 seconds after it starts if your current 
is less than 45A. Obviously this will leave the battery deficit charged unless 
the float current and sun hours remaining can make up this deficit. Reset this 
to zero, the factory default, and let the Min/Max settings control the charge.

Just a note on charging AGM's: My opinion is that the only reliable way to 
properly charge an AGM battery is by monitoring the current to the battery and 
adjusting the charge time accordingly. For this reason, I recommend charge 
controllers that have this function, like the Blue Sky Energy Solar Boost IPN 
controllers. With this method, you can force the absorb voltage to remain as 
long as necessary until the battery reaches 100% SoC.


Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103




On Jul 7, 2012, at 3:53 PM, Mick Abraham wrote:

Greetings, All~

My client's string of SunXtender two volt AGM's won't hold a charge...after 
only two years! The prior AGM batteries also turned to toast prematurely. There 
must be a better way, so could we review the Outback charge setpoints? 

Side note: Delta-v from the highest 2v cell to the lowest shows a gap of only 
.148v during a charge cycle so cell imbalance is not the likely problem. I 
think they're all working together equally bad. 

A small amount of dry powder--light green color resembling verdegris finish on 
copper--can be seen around 30% of the +/- posts, in an amount smaller than 1/8 
teaspoon. From this sign, I suspect that the cells have vented and dried out. 
The property is vacant 90% of the time so I am mostly focused on the MX60 solar 
charge controller as the culprit.

This is an early vintage Outback controller, firmware version 5.11. Temperature 
compensation is in place; automatic EQ is defeated. Bulk & absorption setpoints 
exactly match those requested by Concorde/SunXtender: 28.8 volts 
bulk/absorption & 26.4 volts Float. The controller does regulate at these 
voltage points so it's technically "working"--just grinding up batteries on a 
regular basis.

The Concorde people do not furnish suggestions regarding absorption time or 
"rebulking" so that may be the source of trouble. Controller setpoints have the 
Absorption Time Limit set for "0 minutes minimum & 1 hour maximum". The 
controller is also set to "rebulk" the battery at a 23 volt trigger and there's 
an inscrutable setpoint called "End" that's set for 45 amps. I have a theory 
about the meaning of that but I'll keep the noise level down...

If I recall correctly, the Outback end of charge routine in early days was to 
start a clock & see how long it takes to move the battery to the 
bulk/absorption voltage then apply an equal amount of time for an absorption 
charge before shifting to float. Steve Higgins may confirm if that is indeed 
the protocol for a version 5.11 controller but: has that method now been 
changed in the newer version Flexmax controllers? It seems those now have an 
absorption duration value that can be changed so maybe that's what we need--a 
replacement controller along with good information on the absorption duration 
and/or float setpoints, etc. 

I see that some controllers can even be set to not Float at all. Maybe that's 
better: run the charge then stop it all for the rest of the day. OR: thinking 
outside the box here...what about a controller that won't initiate charge cycle 
at all unless the battery voltage crests down to a trigger point. All I know 
for sure is that two sets of valuable batteries have now been ruined so 
"normal" charge setpoints are not working well in this situation.

If some better electronics (such as blending in the Outback capacity monitor 
gizmo) might help, I'm all ears. Next time maybe I'll suggest flooded cells to 
the client instead of AGM's, but the cells are in a crawlspace that gets 
freezing cold at times. 

Thanks in advance for advice & suggestions. A second off grid client has a 
similar setup so I need to hotfoot it out there and tweak that (more recent) 
Outback controller to match the suggested setpoint revisions...before bad 
things happen again. 

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675
_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





-- 



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to