I have found inspectors agree that if it is labled "Solar only no Load 
circuits" the main breaker protects this panel,  or the sum of the breakers 
does not exceed the busbar rating, the panel is protected without using the 
120% rule
I agree with Kirk 
 

________________________________
 From: Kirk Herander <k...@vtsolar.com>
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org> 
Sent: Tuesday, June 26, 2012 3:53 PM
Subject: [RE-wrenches] combiners and the 120% rule
  

Jason,
 
In your email below you state:
 
“You DO need to observe the 120% rule for the combining subpanel, regardless of 
whether there are loads present, at least in jurisdictions where I have worked. 
I've heard that some inspectors will allow you to ignore it if it is labeled as 
a PV combiner with "add no loads" notation.”
 
NEC 705.12 (D) states that the distribution equipment (in this case the 
combiner panel, fed by multiple inverters and a utility source) must be 
“capable of supplying multiple branch circuits or feeders or both” for (D)(1) 
through (7) to apply. If you fully populated a combiner panel with inverter 
breakers, leaving no slots for load breakers, it is not capable of supplying 
branch circuits or feeders, and IMO the 120% rule does not apply to the 
combiner buss or the conductors back to its point of utility interconnect. I 
have argued this point as well as label combiners “load circuits prohibited” 
(with or without available slots) and received AHJ approval.
 
You could also just lock shut a combiner that had spare slots as a deterrent to 
adding load breakers.
 
 
Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202
 
From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Tuesday, June 26, 2012 8:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase grid tie question
 
I'll email you off-list a 1-line diagram from a system with 164 microinverters 
broken down into 8 strings in a 208V system. This particular system used two 
subpanels to accumulate PV, but that was only because we had to backfeed two 
existing subpanels due to the size of existing 480/208V transformers. You will 
have to look at the utility service and all existing equipment.
 
Regarding the breakers in the subpanel, you will only need a maximum of a 20A 
breaker for each string. The max inverters per string is 25 and the calculation 
for OCPD is:
 
215W / 208V x 25 inverters / 1.732 x 1.25 = 18.65A
 
“You DO need to observe the 120% rule for the combining subpanel, regardless of 
whether there are loads present, at least in jurisdictions where I have worked. 
I've heard that some inspectors will allow you to ignore it if it is labeled as 
a PV combiner with "add no loads" notation.”
 
Use a MLO panel with a fusible disconnect between the subpanel and the 
interconnection point. If you use a 225A panel, you can feed it with 270A. With 
eight 20A backfed PV circuits, you would need to protect the line side of the 
panel with a 100A fusible disconnect. That probably isn't going to work. You 
may be best off from a cost perspective using two 225A subpanels and two 60A 
fusible disconnects. Anything larger than a 60A 3P disconnect and the price 
skyrockets. It all depends on your circuit calculations and the existing 
equipment. Of course, you would need two spaces for your interconnection point.
 
Jason Szumlanski
Fafco Solar
 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org