Bob,

Be careful with that GFDI... It's most likely wired on the output of the 
controllers, on the battery side.

This can trip if a ground fault is occurring, or if you are exceeding 80 amps 
of current.   With 8, 3 module strings, an edge of cloud event you could have 
the 80amp portion of that breaker tripping rather than the GFDI.

Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223



________________________________
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob Clark
Sent: Tuesday, May 22, 2012 7:37 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Finding ground faults

Wrenches:

Sorry to bring up this situation again, but I could not find a previous 
discussion thread that talked about step-by-step procedures for tracking down 
ground faults (I believe it was John Berdner who provided the bulk of the 
writing in that regard and it related to high voltage strings-not that 75-85 
volts per string is all that low).

We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon 
Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner with 
breakers.  The cables from the array are routed to two different Wiley 4-string 
pass-through boxes (located under the two center strings) and then off of the 
roof and into the PV combiner.

Up until this week the system has seen several weeks of awesome power 
production.  Yesterday, the rains came and the GFDI breaker tripped.  Every 
time it rains, the little green breaker on the GFDI trips off.  That tells me 
that the ground fault is occurring in a place where at least one of the 
conductors on one of the strings (possibly more) is getting wet and conducting 
current to ground.

It would seem to me that the most likely place for moisture to cause a ground 
fault to occur in this system would be in the pass-through boxes.  This would 
mean removing the central modules to access the pass-through boxes.

Any of you who have mounted the Silicon Energy modules know that the cables are 
contained in trays along the side of the modules until they are routed through 
conduit to the pass-through boxes.  So, if there is current going to ground 
from any of these cables, it could even be occurring in any of the 9 trays 
along side of the modules.  I do not like the idea of tracking down a ground 
fault in one of these trays as they are all interconnected.

How best (and safely) to track down where the ground fault is occurring?  Any 
advice as to the best and safest way to track down the ground fault(s) would be 
greatly appreciated.

Bob Clark
SolarWind Energy Systems, LLC
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to