In the last list someone mentioned putting the transformer behind the pressure switch for the well pump so it won't be sitting there idling 24/7. It's a good idea, but watch out for the double surge. When the contacts close you'll get a surge load from the well pump trying to lift a column of pressurized water, but also a surge from the transformer as the coils energize. I have seen a few inverters have trouble handling that stacked surge. If the inverter is significantly oversized compared to the pump/transformer it will be ok. Otherwise you can get a time delay relay that waits a second (or so) after it gets actuator power before energizing. In that case you'd want to adjust the pressure switch to come on a few PSI higher than usual so the customer doesn't experience a momentary loss in pressure.

Best,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org