I have seen very hot batteries infact batteries that melted.  and caught fire.  
the problem was that the string was several strings in parallel, and one of the 
strings had thermal runaway.  during charge one battery got hot, and it has 
lower voltage and gets more current. then it get hotter because of the more 
curent. soon it is so hot the other batteries start to discharge through the 
hot battery.  
 
A similar event will occur when one battery in a string of batteries develops a 
bad cell, and the othe batteries in parallel strings will force current 
backwards through the cell.  and thermal runaway occcurs in the hot battery.  
 

________________________________
 From: Jason Szumlanski <ja...@fafcosolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org> 
Sent: Monday, April 2, 2012 11:53 AM
Subject: Re: [RE-wrenches] Hot Trojan Batteries
  

There must be some confusion here about the charging rate. C/20 refers to 
capacity divided by 20, so in the case of a 325aH battery (capacity @ the 20 
hour discharge rate) we’re talking about charging at a 16.25 amp rate. I’m sure 
John is not referring to a maximum rate of 10-15% of 16.25 amps, but 10-15% of 
the 325aH capacity. 
 
Jason Szumlanski
Fafco Solar 
 
 
From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of John DeBoever
Sent: Monday, April 02, 2012 12:14 PM
To: allso...@scswifi.net; RE-wrenches
Subject: Re: [RE-wrenches] Hot Trojan Batteries
 
Jeremy, Wrenches,
 
165°F is definitely too high and you should stop immediately any charge to 
avoid further major problems. I recommend you contact our Trojan Tech Support 
for help at 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
  
 
Below are few perspectives to help the diagnostic:
  
o   System issues:  
ü  Check Charger setting: the C/20 rate mentioned is definitely too high and 
will damage the battery. The maximum recommended current rate is 10-15% of C/20 
for a deep-cycle flooded lead acid battery. Other C/rates are possible but are 
application specific and not typical. 
ü  Check Voltage settings: these are provided on Trojan datasheets, see here: 
http://www.trojanbatteryre.com/Tech_Support/literature.html  
ü  Check Temperature compensation: -0.028VPC for every 10°F above 77°F (add 
0.028 VPC for every 10°F below 77°F or subtract 0.020VPC for every 10°F above 
77°F. See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf  
ü  Check Voltage sensor status and connection. Dedicated wiring is recommended 
ü  Check temperature sensor. It shall be well positioned, typically in the 
middle of the battery bank at the warmest point. 
ü  Check if air circulation between the battery units.  
ü  Check if adequate air ventilation of the battery room. 
 
o   Battery issues: 
ü  C/20 charging rate is too high (see above) 
ü  How old are the batteries? Ageing batteries will face micro-shorts that will 
decrease the battery turnaround efficiency over time that translates in higher 
temperature generation. Typically the battery temperature range is about 20oF 
above ambient temperature, and typical min and max limit are -4°F to 113°F.  
See here: 
http://www.trojanbatteryre.com/PDF/Signature_Trojan_ProductLineSheet.pdf  
165°F is way too high and will damage the units
ü  Maybe you are facing one or more shorted units: check the voltage and it 
will quickly indicate if a unit is shorted.  Shorted units will generate heat 
and will jeopardize the charging of other units. Remove shorted units and 
consult tech support your charger supplier if possible to reconfigure of your 
battery bank with fewer units, configured at a lower battery bank voltage, 
using same voltage settings recommended by Trojan Battery Company.  Typically 1 
to 3 units less would be acceptable, depending the charger manufacturer 
settings. 
ü  Maybe you are facing sulfated batteries, resulting from low charging, thus 
resulting in lower overall turnaround efficiency. This will heat some healthier 
units of the battery bank, accelerating corrosion damages. The max temperature 
acceptable being 113°F, please consult Trojan Tech Support: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
 
ü  Please deal directly off-Wrenches list, with Trojan Tech Support for better 
fine tune resolution: 
http://www.trojanbatteryre.com/Tech_Support/Tech_Support.html?tab=0#TabbedPanels1#top
 
 
I hope this help,
 
John
John F. DeBoever
Global Technical Director – Renewable Energy 
Trojan Battery Company
 
12380 Clark Street  
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 – NY office time zone: USA EST (GMT-5) 
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboe...@trojanbattery.com 
www.trojanbattery.com
  
-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
allso...@scswifi.net
Sent: Sunday, April 01, 2012 7:20 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Hot Trojan Batteries
 
Wrenches,
Can anyone explain why an L16 bank would be at 165F at rest.  Over a C20 charge 
rate, but I have a feeling there might be an internal short 
 
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org 
 
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm 
 
Check out participant bios:
www.members.re-wrenches.org 
 
 

This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure. It 
is intended solely for the use of the individual(s) to whom it was intended to 
be addressed. If you have received this e-mail by mistake, or you are not the 
intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited. If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.   
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to