Adding a capacitor of that size across the inverter's output may cause problems
for the inverter.  Much depends on how the inverter's output voltage control 
loop
is designed, among other things.

Before making any changes of this nature, I highly suggest contacting the 
inverter
manufacturer to ask them what issues (if any) may result from such a 
modification.

In turn, they may request from you more detail about nature of the load the 
inverter
will be powering.  Is it reactive (and if so, what's the power factor)?  Linear 
or non-linear?
And so forth....  It would be helpful to if you have this information available 
before you
call them.


Regards,


Dan Lepinski
Senior Engineer
Exeltech

 
--- On Tue, 3/27/12, Brian Faley <bfa...@magnumenergy.com> wrote:

From: Brian Faley <bfa...@magnumenergy.com>
Subject: Re: [RE-wrenches] Wood boiler ignition issue
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Tuesday, March 27, 2012, 4:04 PM

Hi Kris,  A solution to try would be to add a motor run capacitor across the 
line at the boiler.  10uF-20uf range may improve the crossover distortion 
enough to allow the boiler ignitor to operate properly. Start with 10uF.   
Regards,Brian  Brian FaleyChief EngineerMagnum Energy Inc.2211 West Casino 
RdEverett, WA 98204Ph 425-353-8833www.magnumenergy.com      From: 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kristopher 
Schmid
Sent: Monday, March 26, 2012 11:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Wood boiler ignition issue  Esteemed wrenches,I am 
assisting in troubleshooting a stand alone system with three stacked Magnum 
4448 PAE inverters.  The electric ignition of LP for the wood boiler will not 
fire from inverter power.  As soon as we fire up the generator, the boiler 
ignites.  Has anyone seen this before?  Is there a solution?  The boiler is a 
Central Boiler E-Classic 2400.Thanks in advance!----------
Shine On!Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
NABCEP Certified PV Installer
BSEE 
-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to