Adding a capacitor of that size across the inverter's output may cause problems for the inverter. Much depends on how the inverter's output voltage control loop is designed, among other things.
Before making any changes of this nature, I highly suggest contacting the inverter manufacturer to ask them what issues (if any) may result from such a modification. In turn, they may request from you more detail about nature of the load the inverter will be powering. Is it reactive (and if so, what's the power factor)? Linear or non-linear? And so forth.... It would be helpful to if you have this information available before you call them. Regards, Dan Lepinski Senior Engineer Exeltech --- On Tue, 3/27/12, Brian Faley <bfa...@magnumenergy.com> wrote: From: Brian Faley <bfa...@magnumenergy.com> Subject: Re: [RE-wrenches] Wood boiler ignition issue To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Date: Tuesday, March 27, 2012, 4:04 PM Hi Kris, A solution to try would be to add a motor run capacitor across the line at the boiler. 10uF-20uf range may improve the crossover distortion enough to allow the boiler ignitor to operate properly. Start with 10uF. Regards,Brian Brian FaleyChief EngineerMagnum Energy Inc.2211 West Casino RdEverett, WA 98204Ph 425-353-8833www.magnumenergy.com From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kristopher Schmid Sent: Monday, March 26, 2012 11:51 AM To: RE-wrenches Subject: [RE-wrenches] Wood boiler ignition issue Esteemed wrenches,I am assisting in troubleshooting a stand alone system with three stacked Magnum 4448 PAE inverters. The electric ignition of LP for the wood boiler will not fire from inverter power. As soon as we fire up the generator, the boiler ignites. Has anyone seen this before? Is there a solution? The boiler is a Central Boiler E-Classic 2400.Thanks in advance!---------- Shine On!Kris Schmid Legacy Solar, LLC 864 Clam Falls Trail Frederic, WI 54837 715-653-4295 www.legacysolar.com NABCEP Certified PV Installer BSEE -----Inline Attachment Follows----- _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org