Battery banks can be configured with parallel strings, each string consisting 
of the number of units to meet the 12V, 24V or 48V battery bank voltage 
required by the design. The recommended maximum number of strings in parallel 
is 4.  The lesser number of string in parallel will reduce the chance of 
dealing with cells unbalances, which inevitably occur over time, for the 
reasons you mentioned.  I tend to limit the number of strings in parallel to 1 
to 3 max whenever possible and especially in large battery banks. When push 
comes to shore, for very large Ah capacity applications it is recommended to 
have separate battery banks, each with their own  independent charger, then 
parallel the battery banks  and use blocking diodes.

John

John F. DeBoever
Global Technical Director - Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboe...@trojanbattery.com<mailto:jdeboe...@trojanbattery.com>
www.trojanbattery.com<http://www.trojanbattery.com/>




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, February 16, 2012 11:30 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Quantity of L-16 in a string

Question to the battery wizzs' here and this may have some impact on the 
current thread.-

I was told long ago by a Trojan battery rep. in 1990? that we should not extend 
beyond [12]  L-16s in a bank due to too many connections and to many cells to 
achieve a really go balance on the cell to cell charge.  I have seen this to be 
a reality over the years though I have no concrete evidence other than 
observation. The more L-16s in a bank the more imbalance  or probability of 
imbalance due to the greater of cells and interconnects, points of connection, 
number of strings.

At [12] L-16s I have seen the longest life at 8-9 years and any # of batteries 
beyond it drops off to the 5-7 year range. This is all, off grid observations 
as I have not seen any L-16 wet lead acid in grid tie applications.

Manufacturers could you chime in and wrenches what is your experience?

Thanks

Dana Orzel

Great Solar Works, Inc
E - d...@solarwork.com<mailto:d...@solarwork.com>
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com<http://www.solarwork.com>

"Responsible Technologies for Responsible People since 1988"

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of john
Sent: Wednesday, February 15, 2012 9:18 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] wrenches] Interstate L-16 vs Trojan L-16REB

William,
   Back to the original question you posed.  I have had good luck with 
Interstate L-16 batteries (so far).  My first ones were installed in 2005 so I 
am just at the 7 year mark.  I just looked some today and they are now failing 
at 7 years... one string of 4 real strong and the other 3 strings showing a 
weak battery in each.  This system has been heavily abused with deep cycling 
due to generator problems and undersized PV array (and large loads).  This was 
the system installed in a shed to power construction of a "modest" house that 
turned into a 3 story 5000 sf house and 3000 sf barn with 1200 watts of PV.  I 
added another 1600 watts and now will be adding more along with new batteries.  
I have had lots of problems with the Trojan L16 HC's.  Virtually all that I 
sold (may 5 or 6 systems) had premature failures. (1 to 3 years).  I have seen 
comparable results with the Interstate L16 and the standard Trojan L16, but the 
interstates were considerably less expensive.  I also have an Interstate 
supplier one block from my shop so convenience is part of the plus.  I have had 
a few with leaking cell tops but was able to get instant replacements at no 
charge.   On the question of grid tie, I had a set of 24 Trojan L16's last 12 
years with one cycle per month performed by the owner.  Off grid, however, 
around 7 years seems to be the norm.

John
-----Original Message-----
From: William Miller <will...@millersolar.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Tue, Feb 14, 2012 3:45 pm
Subject: [RE-wrenches] Interstate L-16 vs Trojan L-16REB

Colleagues:



Do any of you have experience with Interstate L-16 batteries?  Are they a

good value?



Thanks in advance,



William Miller



Miller Solar

Voice :805-438-5600

email: will...@millersolar.com<mailto:will...@millersolar.com>

http://millersolar.com<http://millersolar.com/>

License No. C-10-773985



_______________________________________________

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org/>




This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to