Jay:

Thanks for citing this section. I reviewed it just now (2008 version) and I noticed that it says, "capable of supplying multiple branch circuits," not "actually supplying branch circuits." Any energized breaker panel is capable of supplying branch circuits. Only if you size the panel to fit only the inverter breakers could you being to think the panel is no longer capable of supplying branch circuits. Who is to say the inverter breakers could not be "thinned up" to allow future branch circuit breakers?

To my mind, the language is not clear.

William Miller


At 09:38 AM 1/22/2012, you wrote:
Hi Nick,

I see (2011) 705.12 (d) where it talks about " supplying branch circuits as the area where it changes.

ie w/o branch circuits then all circuits are protected by the breakers as long as the main buss isn't exceeded by the solar input of course.

But in putting in that metering device plugged into a outlet, now you have a branch circuit and hence the need to comply with 705.12 (D) 2.

But I could be wrong.

jay
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to