Thank you for all the great interest and the comments on this topic. Here are 
some more details on this project:
 
1. 200 A fused Zinsco Main Switch at the service entrance (45 years old) 
2. Inside the house Square D Split-bus "Main" panel with two 100 “Mains” fed by 
1/0 wire from the outside 200A Main fused switch
3. Next to it Murray 100/125A Sub-panel (Newer, some damage) 
4. Outside Zinsco 125A Sub-panel 
5. In the pool room 125A Sub-panel 
6. In the garage Murray 125 A Sub-panel (newer, looks OK) 

The utility is SDG&E, so no line or load side taps are usually allowed.  On 
another project, we have previously replaced a similar type fused main switch 
with a Eaton Solar Ready Loadcenter with 225A rated buss and 200A main breaker 
in order to be able to backfeed max. 70 A of PV. I am leaning towards doing the 
same on this one....

In this case, I will recommend the customer to upgrade/replace the old Square D 
split bus panel and items 3 & 4. as well. Any other suggestions are welcome.