Hi Kirk,

The Sunny Boy inverters also have a pair of lugs for a single conductor pair 
coming in from the array. They are meant to be used if you have an external 
combiner. No bus bars as you describe are needed.

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk Herander
Sent: Monday, November 14, 2011 2:57 PM
To: RE-wrenches
Subject: [RE-wrenches] combiner bus bar for Sunny Tower DC input?

Hello,

The Sunny Tower has four individual fuse holders on the DC input of each 
inverter. I am combining the array output for each inverter in a combiner box 
before the tower, so there is only a single positive, negative, and gnd going 
to each inverter's DC input. I want to fan this input out to each of the four 
dc fuses via a combiner bus with a single lug and prongs which fit directly 
into each fuseholders' input, ala the Outback combiner bus. Is there something 
similar made for the SunnyTower dc input? I have not been able to talk to SMA 
yet about this. Thanks.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to