I googled "600 volt switch dual throw" and found a cutler-hammer DT363URK.

From 
http://www.alliedelec.com/Images/Products/Datasheets/BM/EATON_CUTLER_HAMMER/416-0447.PDF

Not sure if it carries a DC rating all the way to 600v. 


 



Thank you,

Maverick


Maverick Brown
BSEET, NABCEP Certified Solar PV Installer ®
President & CEO
Maverick Solar Enterprises, Inc.
Office:     512-919-4493
Cell:        512-460-9825

Sent from my HondaJet!

On Nov 9, 2011, at 6:07 PM, "Larry Crutcher,Starlight Solar Power Systems" 
<la...@starlightsolar.com> wrote:

> Right.... a major rewire and many components...and sacrifices. The Outback is 
> limited to 30 amps AC and cost much more than you would need to spend. 
> 
> With my idea you just add a transfer switch....Done. When the grid is down, 
> PV feeds HV CC. Then you can use ANY size inverter, with or without a 
> transfer switch. No rewiring the grid inverter. No 240 volt transformers or 
> dual inverters. No relays, switches or diversion controllers. Batteries are 
> always properly maintained. No phantom loads. Very simple. 
> 
> Thanks for your input. Now if I can just find that darn 600 volt transfer 
> switch.
> 
> Larry Crutcher
> Starlight Solar Power Systems
> 
> 
> 
> On Nov 9, 2011, at 1:55 PM, Drake wrote:
> 
>> Any amount of power will AC couple.  
>> 
>> If you use an off grid inverter, such as an Outback, to feed the protected 
>> load panel, the inverter should be fed by grid AC power to supply loads, 
>> when the grid is available.  Just feed  your grid tie inverter into the 
>> protected loads panel.   You will need a relay to shut off power from the 
>> grid tie inverter when the batteries are full.  This can be triggered by the 
>> fan relay in the Outback. 
>> 
>> The on grid inverter will push power into the grid through the battery 
>> inverter's internal transfer switch during normal operation and AC couple 
>> when the power is out.  If your grid tie inverter is 240 volts, you will 
>> need to use a transformer or two inverters.  
>> 
>> The phantom load of the inverter can be eliminated by using a transfer 
>> switch to send PV power straight to the grid, during normal grid 
>> availability, keeping the inverter turned off.  AC coupling seems much 
>> easier than using a charge controller, but there is no conditioning of the 
>> batteries.  The charge is just on and off at the voltage set point. For a 
>> back up system, that is not much of a problem, as the battery inverter can 
>> maintain the batteries when power is available. 
>> 
>> 
>> 
>> At 02:04 PM 11/9/2011, you wrote:
>>> Nice Find, Drake! Thanks. 
>>> 
>>> What is the minimum system for an AC coupled inverter? 
>>> 
>>> Again, the idea is for low cost battery backup of an existing grid tie. The 
>>> AC coupled schematics I have looked at require a major rewire and many 
>>> components. I would like to hear if someone has a simple add on solution 
>>> compared to just switching the array to the high voltage CC.
>>> 
>>> Larry Crutcher
>>> Starlight Solar Power Systems
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to