William, The tap conductor ampacity must not be less than the rating of the breaker protecting that circuit, which in this case (if I understand the configuration correctly) would be the main breaker in the panelboard.
Any smaller gauge would require its own OCP device of appropriate rating if it's to be code-compliant. Dan --- On Tue, 10/25/11, William Miller <will...@millersolar.com> wrote: From: William Miller <will...@millersolar.com> Subject: Re: [RE-wrenches] Feeder without a dedicated breaker To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Date: Tuesday, October 25, 2011, 2:54 PM Jamie: Thanks for getting me started. I did not think to consider this as a tap, but it appears to match the criteria. William Miller At 11:38 AM 10/25/2011, you wrote: William, I would start with Article 240.21(B). Jamie Johnson
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org