William,

The tap conductor ampacity must not be less than the rating of the breaker
protecting that circuit, which in this case (if I understand the configuration
correctly) would be the main breaker in the panelboard.

Any smaller gauge would require its own OCP device of appropriate rating
if it's to be code-compliant.

Dan



--- On Tue, 10/25/11, William Miller <will...@millersolar.com> wrote:

From: William Miller <will...@millersolar.com>
Subject: Re: [RE-wrenches] Feeder without a dedicated breaker
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Tuesday, October 25, 2011, 2:54 PM



Jamie:


Thanks for getting me started.  I did not think to consider this as
a tap, but it appears to match the criteria.


William Miller





At 11:38 AM 10/25/2011, you wrote:

William, I would start with Article
240.21(B).


Jamie Johnson

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to