There are yet other issues to consider relative to specific gravity.

#1:
I believe temperature has been mentioned already, but merits revisiting:

Specific gravity varies somewhat with the temperature of the electrolyte.  Some 
of the
more sophisticated measurement equipment takes temperature into account.  Lower
cost models don't.  However, temperature can be included in your calculations 
by use
of a simple thermometer to measure approximate battery temperature at the time
the SG readings are taken, then factored into the readings.  Cold batteries 
will yield
higher SG readings than warm ones.


#2:
Another concern is stratification.  Acid is more dense than water and thus 
sinks to
the bottom of the battery.  For more accurate readings, electrolyte must be 
"stirred"
to thoroughly re-mix the solution *before* samples are taken for SG measurement.
Given the construction of batteries, this is difficult (but not impossible) to 
do.  Failing
that, and using just an initial sample of electrolyte from the top of a cell, 
SG readings
from the top may be lower than actual values.

Jamie Surrette recommends adding distilled water to bring the electrolyte level 
up
to the manufacturer's recommended level, then charging the battery to a point of
light-to-moderate outgassing (with all precautions, of course) for a couple of 
hours.
After the battery has rested for as long as possible (24 hours suggested), 
*then*
take a SG reading.  Hydrogen and oxygen get trapped in the electrolyte and will
cause errors in any SG readings taken immediately after such a charging period.

Since this is an off-grid home, one option might be to charge with the generator
as late into the evening as possible, then take SG readings the next morning
before any significant loads are applied.  May be a Friday night/Saturday AM
event if the owner works during the week.


Dan


--- On Mon, 10/24/11, Allan Sindelar <al...@positiveenergysolar.com> wrote:

From: Allan Sindelar <al...@positiveenergysolar.com>
Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Monday, October 24, 2011, 5:35 AM

Ron,You have made a connection that I would not have made, and while I may be 
wrong here, it has got me thinking. I have never equated low water level with 
SG, nor have I ever read in battery maintenance guides that I should maintain a 
particular water level before measuring SG. I'm not convinced that electrolyte 
level has any connection with measured SG, although it would seem logical on 
the surface. I have always thought that if the correct concentration of acid 
was installed at the factory and not lost thereafter (such as due to a spill or 
chronic overfilling), the SC is only a function of SOC. I'm interested in 
others' opinions here.

AllanPositive Energy
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org