Eric,

We have had excellent results doing these with Sunny Boys and Sunny Islands. It is more pricey but if you have a high end customer and want a a reliable, trouble free (?) system, we have had no wrinkles or call backs with this approach. We have inverted at the array in the past and sent AC to the critical loads sub panel at the house and from there to the Sunny Islands and then either the main service panel or done a tap between the main service panel and the utility meter. If you do a tap then you need an AC fused disconnect before the tap. But you could also run DC from the array to the house, if it is a new system, and then invert to AC. This is also a good approach if a customer wants to add battery back up to an existing grid tie system. There is some rewiring but it is not at the array. The output of the grid tie inverter in an AC coupled system needs to land in the critical loads sub panel rather than the main service panel where it probably now lands.

Magnum has a good schematic on their website showing how this is done using a MS-PAE battery based inverter and a grid tie inverter

Larry Brown
Sun Mountain
Nabcep Certified PV Installer


On Oct 2, 2011, at 12:15 PM, Eric Thomas wrote:

Wrenches,

We are designing a super high end grid-tied w/ battery backup system for a customer. Array will be ~15kW; pole or stand alone structure mounted; 250' from home/batteries. My question is: does it make any sense to invert the power at the array and use this ac to make the long run to the batteries THEN connect to a typical battery charger rather than a dc charge controller? Im mostly concerned with huge dc conductors making this run across the property. Havent delved into the specific design enough to size said conductors yet, or specify any equipment, but wanted to know if im barking up the wrong tree ir not.
Thanks for the insight.

Eric Thomas
Founder
Solar Epiphany LLC
NABCEP Certified PV Installer
WA Electrical Contractor # SOLAREL911NR

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to