Thanks for the input, all!  I can't wade to dive into this project, now.

On Fri, Jun 10, 2011 at 8:53 AM, Max Balchowsky <m...@seesolar.com> wrote:

> Kris, I worked traffic signal systems for years, we spliced conductors in
> pull boxes that fill with water on a regular regular basis. There are
> products available that are rated for waterproofing connections and the
> THWN-2 is rated for wet locations, but I don't know about submersed
> locations.
>
> Max Balchowsky
> Design Engineer
> SEE Systems
> 1048 Irvine Ave Suite 217
> Newport Beach, Ca. 92660
> 760-403-6810
>
>
> ------------------------------
> *From:* Allan Sindelar <al...@positiveenergysolar.com>
> *To:* re-wrenches@lists.re-wrenches.org
> *Sent:* Thu, June 9, 2011 6:48:32 PM
> *Subject:* Re: [RE-wrenches] Underwater wire
>
> Kris,
> I don't know a Code-compliant solution, having not faced this. But I'll
> suggest that you not attempt to glue and seal conduit to keep the conductors
> dry, as it won't work permanently. Use wet-rated wire, expecting any conduit
> to provide only physical protection. THWN is wet-rated - that's the W. You
> might consider submersible pump cable also.
> Allan
>
>  *Allan Sindelar*
> *al...@positiveenergysolar.com* <al...@positiveenergysolar.com>
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> *www.positiveenergysolar.com* <http://www.positiveenergysolar.com/>
>
> *
> *
>
>
> On 6/9/2011 7:31 PM, Jesse Dahl wrote:
>
> There utility companies up here in northern MN bring power to islands all the 
> time. The have cable underwater. Maybe contact Minnesota Power....
>
> Jesse
>
> Sent from my iPhone
>
> On Jun 9, 2011, at 3:48 PM, Nathan Jones <solardud...@yahoo.com> 
> <solardud...@yahoo.com> wrote:
>
>  Kris,
> We work on boat docks on army corps of engineer lakes frequently and they 
> have wire in direct contact with water everywhere. The lakes here are flood 
> control and fluctuate a lot, like 50 feet in a given year. The marinas are 
> dragging the feeder wires all over the place on rocky bottoms. We kill very 
> few people with this insane practice but as the feeder wires age I believe 
> the fatalities will increase. This is ground referenced service in fresh 
> water with poor conducting capability in the water. Very dangerous yet 
> allowed.
> Your situation would be quite safe IMHO as there would be no stressing of the 
> delivery system.
> Nathan Jones
> Power Source Solar
> 417-827-0738
>
> On Thu Jun 9th, 2011 2:30 PM CDT Kristopher Schmid wrote:
>
>  I have an installation that is a ground mount on a berm with a man-made pond
> between the array and the BOS.  The pond is about 4 feet deep.  How would
> you wrenches make this run? in weighted conduit with primer and glued
> joints? use boring and go under? out of conduit with wire directly in the
> water?
>
> Does code have anything to say about this specifically?
>
> Thanks as always.
>
> --
> Thanks,
> Kris Schmid
>
> Legacy Solar, LLC
> 864 Clam Falls Trail
> Frederic, WI 54837
> 715-653-4295
> www.legacysolar.comsol...@legacysolar.com
>
>  _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>  _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Thanks,
Kris Schmid

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
sol...@legacysolar.com
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to